On the occasions when I need to run the welder everything else can be shut off.
I mentioned the loads from the house only to communicate that the house loads will be pretty light. I plan on eventually building either a wind or a hydro system to keep the batteries charged, but that takes time. In the short term I can run everything off the diesel and have plenty of power with less work.
Because of the altitude I will lose about 21% of the engine's rated horsepower.
Therefore I was thinking of using a 20/2 Listeroid and a 12KW FuKing head. Is this going to be too much generator and drink me out of house and home?
Your Lincoln welder is the type I intend to purchase. So lets build in a saftey margin and assume I need 4KW to run a welder.
The Metro 20/2 running at 650 RPM makes 12 HP but when derated 20% for altitude only produces 9.6 HP. According to the chart at http://www.power-co.net/mighty_yanan_generator.htm I should run a 5KW head.
If in fact there is not a significant penalty in running a larger head than needed I can run a 10KW head. That way if I need more power at some point in the future I can, change the pulley on the generator head and run the 20/2 at the full rated speed of 1050 RPM.
The 10KW head would also be good if at some point I moved the generator to my other off grid property at a lower elevation.
Now I understand the reasoning behind why John recommended buying the 20/2 with a 10KW head. [ Parent ]