Inverter question | 9 comments (9 topical, 0 editorial)
Re: Inverter question (3.00 / 0) (#2)
by richhagen (richhagen (a t) Juno.com) on Fri Oct 3rd, 2008 at 07:24:50 AM MST
Inverters such as Xantrex SW series and Outback's FX series have an 'LBX' mode that will switch between passing grid power through the inverter for the loads when the batteries are low, to powering the loads from the batteries when they are higher.  It is an either/or setup, basically synchronizing the frequencies and switching the power source from grid to batteries or vice versa.  On the Xantrex model I have, and those I have seen, you can not turn off the battery charge function which draws power from the grid to charge the batteries when they are low, but you can turn adjust the charge amps down to about 2 amps if I recall correctly.  I have never rigged an Outback Inverter in this way, so I don't know about switching off the battery charger while in this mode.    Like Flux says, I do not think it would be possible to do what you are asking about without calling it grid tied, so this 'LBX' mode is about as close as I can think of that you can get with a commercial inverter. I recall that Xantrex indicates in their manual that you generally do not need Utility approval to operate in this LBX mode as you cannot feed power back into the grid.  Rich
Re: Inverter question (3.00 / 0) (#3)
by richhagen (richhagen (a t) Juno.com) on Fri Oct 3rd, 2008 at 07:27:30 AM MST
The utility approval part is probably mainly for the U.S., since I see you are using 50hz power, I will assume you are somewhere else, so you should check your local regulations before using an inverter in that type of mode.  Rich
Re: Inverter question (3.00 / 0) (#4)
by boB on Fri Oct 3rd, 2008 at 11:26:01 AM MST
(User Info) http://bob.gudgel.org
LBX mode just switches on the charger when the battery voltage gets below a certain point.  This is what you want I think.  No utility blessings needed as far as I know.
boB
Re: Inverter question (3.00 / 0) (#5)
by Flux on Fri Oct 3rd, 2008 at 12:16:17 PM MST
That is an option that I didn't think of. If you can manage a lot of the time on the inverter and the inverter can supply all your needs then you can use the grid to charge the batteries when you are low on power. This solves all the problems of change over.
The efficiency will be lower than using grid power direct but if it is only a small back up occasionally the convenience will make it worth the trouble.
Re: Inverter question (3.00 / 0) (#6)
by ghurd on Fri Oct 3rd, 2008 at 12:38:32 PM MST
I am working on my "ghurd kit" to do that, set at 12.2V or so to turn on a standard grid powered battery charger until a considerably higher voltage.
Seems to be OK so far, but long sloppy bare wires shorted and fried something related to the relay.  A bit concerned about the battery being grounded in North America, have not had time to get it sorted out.
Re: Inverter question (3.00 / 0) (#7)
by TomW on Fri Oct 3rd, 2008 at 01:25:16 PM MST
boB;
I use "HBX" [High Battery eXchange] mode on my FX2524 [perhaps incorrectly] It will go on grid to keep batteries safely within their voltage limits by going on grid, charging the batteries and powering loads from the grid and then dropping the grid when the batteries get to a set voltage. I run certain loads off the inverter and it helps me sleep at night knowing the loads will be supplied pretty much regardless of my incoming RE levels. My tired batteries just don't have a lot of bottom to them so on long stretches of low RE it keeps things on the inverter using all the RE there is then going to grid charge as needed.
Just how I do it with an Outback here. You need a "Mate" to do this I believe. For sure to set it up.
Mileage may vary.
Tom.
Re: Inverter question (3.00 / 0) (#8)
by boB on Fri Oct 3rd, 2008 at 11:05:19 PM MST
Yeah, HBX,  LBX,   same thing...  Trace called it LBX, OutBack calls it HBX,
but it's the same idea.  Use renewable energy whenever possible.  Use the grid
as little as possible.  If the batteries are not so good or you just want to
be good to them, adjust the settings as good as they'll let you I guess.
Other systems without LBX/HBX have to be made specially with a separate
relay and control etc.  It's nice to have it built into the system.
boB
Re: Inverter question (3.00 / 0) (#9)
by TomW on Sat Oct 4th, 2008 at 04:33:34 AM MST
boB;
Thanks for the clarification. I thought I had somehow remembered the "H" wrong. Nice to know I can actually trust the occasional memory!
I do like how the Outback with a Mate turns a fairly "simple" inverter into a clever piece of gear. It does come at a price, however.
Thanks for the response / info.