Re: Problems with Preexisting Hydro
(
3.00 / 0
) (
#16
)
by 74VDC on Thu Aug 28th, 2008 at 02:04:38 AM MST
(
User Info
)
OOOPS!
Just reread the initial post and I see it was 40' head and a 420 foot long penstock....ok, now that certainly makes a difference.
Still I'm coming up with 5.42 kW.
So after generator losses I get 1.63 kW.
The 420 feet of penstock friction, runner damage, possible slight nozzle misalignment (I know this is critical)and other deducting factors would account for some loss for sure. Your measured current at generated voltage is barely breaking 100W.
The batteries may pull down the voltage depending on their state of charge, but while doing so, current will increase. I like to get things simple and unmistakable for testing things like this. I'd get several 5 0hm wire wound ceramic resistors along with several other smaller higher value resistors and putting them in various connections of series/parrallel begin making measurements for optimal power. I would do this because I have all this stuff.
I live in Maryland and we have net metering, so I'd never consider charging batteries, but instead grid tying. You will lose so much power with batteries it isn't even funny. Far, far more than a grid tie inverter.
I still cannot imagine expecting only 240W with 120 gpm and 40' of head. I also have a hard time beleiving so much drop on your xmission line, particularily with DC, but 630' is a long, long way at 15v. I'll crunch the numbers later when I can look of the circular mil area of 2/0 and specific resistance of Al, although I think it's 17.7 and soft drawn Cu is around 10.4 I think.
I do not fully understand your set-up or what you're exact goals are.
You seem to be set on DC, so why then did you spend $600 on triplex...were you wanting the possibility of future 3 phase?
If you really think you have line loss issues parallel the old #8 AWG conductors alongside the 2/0's...just for temporary test purposes...I'm thinking you're gonna see little difference. If it turns out that it helps...get some al/cu connectors, Penatrox and leave it. It would not be code approved, but unless you grid-tie your not subject to the NEC, besides, there are numerous paralleling provisions in the NEC for instances such as these. You could have saved a bundle of cash by utilizing the #8's and paralleling to begin with. You're voltage is low, but so is your current.
I'd find a good 30VDC PM genny like another poster suggested....like fast!
[
Parent
]
Problems with Preexisting Hydro
|
16
comments (16 topical, 0 editorial)
Menu
·
create account
·
How to use the board
·
FAQs
·
search the board
·
Google search the board
·
Old Otherpower Board
Login
Make a new account
Username:
Password:
You must be a registered user to post here. It's easy and free, and the link is on the upper right side of your page.
All trademarks and copyrights on this page are owned by their respective companies. Postings are owned by the poster, but may be deleted or moved at the ADMIN's sole discretion. The Rest © 2003 Forcefield.
You can Email the board ADMIN here
. PLEASE include the username you signed up with!