Fisrt diary post: house description and tentative flow diagram | 24 comments (24 topical, 0 editorial)
Re: house description and tentative flow diagram (3.00 / 0) (#10)
by mbeland on Wed Apr 23rd, 2008 at 07:23:11 AM MST
Thanks for your comments Scott,
You say 2 inch styrofoam is not worth it and above gradee it is not enough. Our soil is rather humid. We cannot assume the slab would have been dry. Above grade is only 6 inches.
You say the tank is too small. I guess it is time for me to actually pickup the calculator and actually calculate load. I think the way I should do this is by analysing my electric bill. Will post again on that. The tank I plan to use is in my mind pretty big (4 x 4 x 8 ft)! That would surely take a fair bit of space in my technical room...
Regarding code and antifreeze, from what I understand, canadian code requires double wall heat exchanger unless there is more pressure in the domestic water line than in the antifreeze side. That is why I assumed it was OK.
Martin
Eau, soleil, le vent
Re: house description and tentative flow diagram (3.00 / 0) (#13)
by BigBreaker on Wed Apr 23rd, 2008 at 09:16:57 AM MST
4x4x8 seems big and water retains a lot of heat energy per delta T but space heating requires enormous amounts.  A 100k BTU/Hr furnace is equivalent to 33k watts of electric heating.
You suggest a 128 cubic foot tank.  That's 3.6k liters of water at 4.2kJ per liter per degree C or 15.1 million joules per degree C.  But that is only 15.1k BTU per degree C.  A (small) 100k BTU/Hr heat load will "eat" over six degrees out of that tank every hour.
You need a bigger tank or a phase change material like sodium acetate trihydrate.