Hi Sparweb,
Yes I wondered if the SI does what it is supposed to so on the 30th March I did a test by altering the SI frequency and seeing what leaks through from the Sunny Boy.
I restarted the SI on 52, 53 & 54Hz under constant PV of approx. 360W as it was a dismal day.
Using just one SB3800 AC Grid tied to the SI AC1 input/output.
at 50Hz SB shows 360W Output.
at 52HZ SB showing a 63W output.
at 53HZ SB shows a 43W output.
at 54HZ SB shows a 34W output, and then tripped out showing disturbance. This is what it is supposed to do, as at 54HZ the SB agrees with its internal settings that are set when in Island/Off Grid Mode.
I swapped Sunny Boys, and tried a SB3000 AC Grid tied to the SI AC1 input/output.
at 50Hz SB Showed 420w Output.
at 52HZ SB showed 0W Output.
I have left the SB3000 still connected as this SB doesn't leak, but still the Frequency goes 'Nuts'.
So I believe the SB's are NOT giving the SI problems, and the SB's shut down as requested when the SI 'UP's' the Frequency as Specified. So that bit works.
(Note, The SI is 150 yards from the SB, so I had to run, run ,run, well it amused the locals here watching the Mad Man running up and down French fields. phew!.)
The Fault seems to be around the SI's Charging regime that is linked to the battery voltage, and the SI can not differentiate between what the battery is doing and what voltage is coming in and out of the SI.
The SI has a shunt sensor on the negative cables between the battery and other DC Controllers /charge sources, and is supposed to see all the ups and downs of these and amend accordingly.
Now I can watch the battery being charged or giving loads on the real life display screen, so the amperage can be seen going + or -.
But My SI will not have any of it. Battery rises just above SI Float setting, 'Wham' away goes the frequency.
Checking with other SI owners around the World, Like Stephen in Spain, ...........
"My 5048 which is only DC coupled using a non-SMA charge controller. The charging schedule and voltages of this external controller are in no way synchronised with the SMA, so it spends half it's time wanting to FLOAT when the charger controller is doing a bulk, absorb or even an EQ. This has no effect on the SMA's frequency"
And from a SMA SI Installer in Scotland
......"I don't remember ever seeing 60Hz though. It's quite likely you have a dud inverter. Operating with DC charging sources is quite normal and should not present either of the issues you are seeing.â€So Purchasers of the new all singing and dancing SI6.OH-11, beware, beware, battery voltage just a little to High, your Inverter Frequency goes 'NUTS'.
And as Lisanne Schneider, of SMA Service has said,
"But the Sunny Islands now give out an inverter frequency up to 60Hz if there is still energy going into the batteries.
This is not a mistake of the current firmware version."What next?