The math looks right to me. I'll just add a couple of thoughts if they're not apparent. When Damon says "sets", really what we are talking about are series strings. If you put two batteries - of the same age, voltage and type - in series the voltage doubles, but you have the same number of AH as the nominal rating of each. If you put them in parallel, the voltage stays the same but you get 2x the AH rating of the individual batteries.
There are some maintenance factors when you get too many parallel strings. If the application is such that you need more power, increasing the voltage of your bank is probably a better choice in the long run.
Also, while the kWh units are correct, in reality you only want to be discharging the batteries to about 50% (or less) of their capacity, so the usable storage is about half that stated.
best, ~ks