Author Topic: Replacing my gel batteries  (Read 5153 times)
« on: September 09, 2017, 06:29:46 AM »
It doesn't seem nearly long enough ago since I bought my ~400Ah of 12V gel batteries for my off-grid system.
http://www.earth.org.uk/expanding-off-grid-PV-system.html
A year ago I wondered if I'd killed them a year ago, and I'm still wondering.  Anyhow it might be time to bite the bullet and replace them.
Given that loads are low (from less than 1W average for my core server load, to ~16W when taking networking gear off-grid to maybe 60W peak when powering my laptop occasionally) any sort of battery would supply the discharge current.  The primary aim is to keep my server off-grid through winter, and take other loads off too as above where possible.
I have a nice Morningstar SS-MPPT-15L charge controller for the primary array, and a cheap Chinese PWM controller in parallel for a small amount of 'extra' PV.
Question: AGM or gel for the replacements?  I know the gel should have the longer service life, but I wonder if chucking up to 15A+ peak charging current at it is what is finally killing it off, and if AGM would be more resilient?
Simen
  • Country: no
  • Grimstad, Norway
Re: Replacing my gel batteries
« Reply #1 on: September 09, 2017, 07:12:45 AM »
Go for a 12V LiFePO4 bank. :)
You could manage with half the Ah, without sacrifice lifetime vs. LA-batteries...
« Reply #2 on: September 09, 2017, 07:38:34 AM »
Thank you.
I'm not against LFP at all, as you see, and I'll eventually do that alongside many more kWh grid-tied for my house I hope, but for now there doesn't seem to be a good choice of solar LFP controllers*.  In fact, many of the BMSes seem to be totally proprietary and opaque.
Eg something that is MPPT and will work with my 60-cell PV panels and won't blow up with excess available input power!
But please show me that I'm wrong: I'd be happy to take that route.
« Last Edit: September 09, 2017, 11:57:46 AM by DamonHD »
Simen
  • Country: no
  • Grimstad, Norway
« Reply #3 on: September 09, 2017, 11:47:36 AM »
I agree; there are not many (if any) solar-controllers there that really supports LFP - but most lfp-batteries would do ok with standard controllers set to 14.4V CV, as a proper controller would keep the voltage at 14.4V until the battery draws only a few amps. The BMS in the lfp-battery should manage the balancing just fine, but might struggle a bit if the cells are badly out of balance. A simple solution would be to connect a CV source for some hours, once a month, to let the bms fine-balance the cells.
I've run a 12V, 110Ah lfp battery in my caravan for a couple of years now, connected to a 15A MPPT controller and 160W of panels, and i checked the balance of the cells a month ago, and they were spot on. There is a constant load of 7Ah/day, year round (a smart-home controller and an AP) - and higher when i use the caravan. :)
« Last Edit: September 09, 2017, 11:54:11 AM by Simen »
« Reply #4 on: September 12, 2017, 03:02:12 PM »
No more opinions?
In my situation is there any significant difference between gel and AGM?
« Reply #5 on: September 12, 2017, 04:12:06 PM »
Damon;
Have you thought of other battery chems? OR are these the most cost effective available?
Writing a BMS using a arduino should be child's play for you.
I'm still using my NiCDs and am getting ready to bring up another 40Ahr of them. I have gone back and re-done the packs into 11batts/setup , makes for less voltage drop and closely matches the charging regime for the solar chargers.
Hope this doesn't muddle the mix further.
« Reply #6 on: September 13, 2017, 02:02:13 PM »
Hi Bruce,
I just don't think that I can get good 60-cell MPPT into any other manageable chemistry at the moment.
Next round yes, when my Morningstar controller will be old hat and out to pasture along with me!
But again, please show me I'm wrong!
« Reply #7 on: September 13, 2017, 02:59:57 PM »
Damond;
In my thinking, the charging profile for the MPPT using 60-cell for 12Vdc and a good set of NiCDs (recycled or new) would be very similar to the AGM style LA batts.
There is still quite a stigma about NiCds but in reality the NiCDs are very safe with someone who won't go throwing them in the fireplace.
In your case, since I don't know if you have a good source for used NiCDs , going with AGM is probably your best bet. I do have several of the AGM work had just lying around 6Vdc 7Ahr , these are nice little units and will probably be used in front of my NiCDs once I've had time to sort them out.
I can say for certain AGM are used in all the UPSes I've had the fun times of working on. APC, Eaton, MGE all use AGMs . This is includes the units with 110Vdc on the buss.
Hope this helps
« Reply #8 on: September 13, 2017, 03:25:34 PM »
Thanks!
« Reply #9 on: September 14, 2017, 05:46:55 PM »
Plop a decent sized lead acid on the charge controller then run the lithium BMS off that...
« Reply #10 on: September 15, 2017, 04:29:08 AM »
I sorta kinda was doing that before.  But still, should that new LA be gel or AGM?  B^>
mab
« Reply #11 on: September 15, 2017, 07:31:24 AM »
My vote would be agm, although I'm not sure I have enough experience of gel to make an informed decision. My agm is still going 12+ years after I bought them 2nd hand, although I did follow joestue's (?iirc) advice and watered them a few yrs ago which helped, and getting the hydro running means they've been operating mostly as standby/ surge for a few years which is what they were originally built for.
« Reply #12 on: September 15, 2017, 11:30:22 AM »
Yes, making the bank last 12 years would be good: we'll be well into Lithium-air or something by then!
PS. Keep the ideas coming!
clockmanFRA
  • Country: fr
    • Renewable Energy creation
« Reply #13 on: September 16, 2017, 06:00:41 AM »
Hi Damon,
Just returned from your neck of the woods in London, spent most of my time at traffic lights. haha.  Also got funny looks from the locals with my very French Normandy mud covered 3 year old Toyota, when I parked at my clients. Note to self,...... remember to take wheelbarrow for the Parking charges next visit !!!!!
I haven't commented on your batts, as there are a lot of very wise guys here that have oodles of more brains and experience.
However, .... I thought that I would share my last 10 years of experience with used/second hand AGM's, (real ones with soaked matt plate separators) and Sealed Lead Acid, SLA.
This summer I purchased and installed over a ton of New SLA batteries, they were called marine types Ultra deep cycle.
http://www.ebay.co.uk/itm/4-X-12V-110AH-Deep-Cycle-Battery-Numax-XV31MF-Leisure-Caravan-Marine-Boat-/191830670926?hash=item2ca9ffbe4e
2017 my Installation is now ....  a 48v 1300ah battery system, strings of batteries with copper plate/strap inter links and main 16mm battery cables are all just about the same length.
Firstly ..... I had tested 12 of those New SLA  for the last 5 years and they had all behaved very well and staying remarkably stable with at rest voltages and loading voltages. In the old photo below there are 8 up the top on test.
Up top as they only weigh 25kg each, lighter than the equivalent ah AGM's
Secondly ..... The Photo is 5 years old showing my test installation, ....... My previous used/second hand AGM's MARATHON, and those Blue ones in the Pic, forgotten there 4 letter name, were bad bad. In every day use Lasted between 1 year and 5 years, then they would no longer hold more than 12.2v after 24hrs rest period.
Most would loose a cell, either the first or the last, as the plates inside had only 6 -10mm clearance, and any buckling would have the cell rise slightly and connect with the main link bars, and that was that. And yes I took a couple apart to look see. (but folks remember there is ACID in there, in the matt separators).
The exception is those yellow POWERSAFE (Hawker Siddley) they have behaved well, five years down the line.
Those Used Second hand YUASA 6v 160ah SLA have also behaved very well over the past 5 years. The only drawback is there 6v and therefore need some careful cable connections.
Thirdly...... I got fed up with constantly monitoring those used/secondhand AGM's, but being short of large amounts of cash, found that NEW SLA cost about the same as the so called refurbished AGM's, In the Uk anyway. Hmm, this was becoming a no brainer, but what New make was the best? at the best cost? and best weight?
Fourthly......... and importantly for me, was a comment from 'Oztules' ........
"Lets be clear, there is no need for a monster battery or an expensive battery, better to use golf cart ones that will last 5 years, and replace them every 5 years.
6x220ah American batteries can be found for $200, so a 24 battery bank will only be $5000 ( you will probably get more years than that as they will rarely be discharged beyond 25%... and that should give 3000 cycles)
Stylish expensive cells ( whilst I like them very much) are not necessary to produce a better system."
So hence with me going down the Leisure battery route, but I deliberately never discharge beyond 10%.
So far my testing and monitoring has revealed some interesting points, especially as I have moved down the OzInverter route, with the  OzInverter back charging and the AC coupling, where the battery bank does not have to be so massive as the GTI's feed directly into the OzInverter created AC output MINI GRID so the battery bank is not being heavily drawn upon.
Damon, Just my opinions and observations on a Simple, Robust and very Cost Effective solution that suits my situation.
« Last Edit: September 16, 2017, 06:09:00 AM by clockmanFRA »
« Reply #14 on: September 16, 2017, 08:32:36 AM »
Many thanks for that view!
I've adjusted the thresholds up a long way just now to try to be kinder to the battery bank, and I may do more
subtle stuff like raising them further in prolonged dull periods:
http://www.earth.org.uk/expanding-off-grid-PV-system.html#LESS_DoD
Right now that has pushed my bank from being in an apparently 'OK' state to 'VERY LOW', and the system should draw much less juice from it until the SoC rises significantly.
(BTW, when people ask me if I miss ever having owned a car, your experience of parking and charges is one of the reasons not!)
« Last Edit: September 18, 2017, 02:36:16 AM by DamonHD »
Rainwulf
« Reply #15 on: February 05, 2018, 03:43:19 AM »
No more opinions?
Gel is less "forgiving" then AGM for overcharge conditions, which is one of the reasons i would pick AGM over Gel if i had the choice.
Honestly, flooded is my number 1 choice if you dont wish to go the lithium route, or even look at what modern nickel-iron cells could do.
« Reply #16 on: July 04, 2018, 05:00:18 PM »
Thanks all.
(I nearly have time to breathe again now that we have taken our production code branch...)
I tweaked the control algo to explicitly estimate SoC, allowing for temperature and some internal resistance, and use that to decide when to drop the 'dump' load back to grid.
The upshot is that the battery still doesn't get below ~12.5V but I am now getting my target 500Wh/d through the system and removed from the grid.  We'll see how well this changed scheme holds up mid-winter.
So maybe I didn't quite kill these gel batteries after all.
« Reply #17 on: July 05, 2018, 11:50:18 AM »
Damon;
Good to see you posting again.
« Reply #18 on: July 05, 2018, 02:12:43 PM »
Still silly busy, but the focus will shortly be moving away from the core tech into parts of the work that others are concentrating on ... except we have a whole new big project starting RealSoonNow(TM), like maybe yesterday but the paperwork hasn't arrived yet!
« Reply #19 on: July 06, 2018, 08:51:07 AM »
Damon;
I've been watching your OpenTRV and TRVRobot posts for quite a while now.
While talking with a few of the smart-house builders here in St Louis, an interesting topic popped back up that stems from several years ago when the Smart-house concept really starting taking off.
While insulating the homes to both lower the bills and lessen a single houses impact on the environment, there is the problem with bad air in the ultra-tight houses. They're now using a term that solar warmed water/glycol users know all to well. "Stratified"
Have you given any thought to stratified air issues? With a home that is ultra-tight there is the issue of possibly having stale (stratified) air in the home.
Our home namely Living and dining rooms are so tightly sealed there is no natural air movement, therefore I built a solar powered 12Vdc fan system that moves the air around. We could tell the difference!
While our energy bills have dropped to 3/4s of what it was. Until I built that air mover, it was way too stuffy even with it at 20C.
 I understand your systems are boiler based, however, even during our heating season we felt the air get stuffy once the forced air stopped moving air around.
Any Thoughts?
« Reply #20 on: July 06, 2018, 09:32:00 AM »
"Built it tight, ventilate right" is the manta.
Part of getting a design right IS to ensure that airflow is good in such a home, eg draw stale air from wet areas at ceiling height and return to living and sleeping areas at the right temperature at the right height, whatever that is.  Preferably using MHRV (mechanical heat-recovery ventilation) to maximise energy efficiency.
« Reply #21 on: July 06, 2018, 12:24:20 PM »
And ... I'm getting to test the temperature compensation in the solar controller and my code.  31C in the shade outside now, 29C measured at the battery!
http://www.earth.org.uk/out/daily/B1T.png
« Reply #22 on: July 06, 2018, 02:15:01 PM »
It'll be interesting to see what the programming does!
Good thing that not the inside temps!