trace d2424 problems
By bob golding, Section Controls
Posted on Fri Jul 10, 2009 at 10:21:11 PM MST
anyone had this problem before?
my trace d2424 inverter/charger has stopped working. it was working fine until i tried to  use it in charge mode. i am using it with a 5 kva diesel genset. what happened was when in charge mode the transformer growled for a around 30 seconds then it would lock and start charging normally. the last time i tried to use it it refused to lock and then blew the fuse to the generator. now when i connect it a relay clicks and then it refuses to do anything else. anyone got any ideas,or better still a link to any schematics. i have yet to look at the waveform from the generator but i know it will be pretty horrible.
cheers
bob golding
trace d2424 problems | 1 comment (1 topical)
Re: trace d2424 problems (3.00 / 0) (#1)
by dnix71 on Fri Jul 10, 2009 at 06:04:15 PM MST
This is a DR2424? There is no Xantrex d2424 listed on the web.
http://www.aaasolar.com/ProdLit/Trace/DRManual.pdf
First according to Xantrex' manual, there is a 40 second delay before it switches from inverter to battery charger (page 15). That is to allow the generator to spin up and stabilize. It will work as an inverter or charger but not both at the same time.
Second, the peak voltage of the generator determines if it will charge you batteries. (page 20) There is a 10 to one step down on the charge circuit transformer, so if the peak voltage of your genset is lower than 130 it won't work at all.
Third, I hope you didn't do this, but if you hooked up your genset to the ac output side, you must reset the Trace inverter. If you do that too many times it will blow the inverter. (page 14).
  67 Scoop users have viewed this posting.
· Also by bob golding