Wire sizing for Western North Carolina hydro project
« on: January 12, 2006, 02:46:06 AM »
Hello I live in Western NC and am working on a microhydro project. I am going to run 2200 ft of wire and would like to have a 3% or less loss. The hydro machine is producing 1200 watts(HV 1200 (3 phase) from Harris Hydro and HydroInductionPower.com) and will transmit at 480 volts. I am trying to figure out the appropriate wire size for this venture. I would like to keep loss to around 3% and would like to know the math process behind it. Here is one of the ways I have had it presented to me . . .


____________________________

From Table 8 of NEC resistance of #10 (7/19) wire is 4.070 ohms /1000' (times) 4400 ft (2200 doubled) = 17.908 amps times 2.5 amps (1200 watts) = 44.7 volts drop

Divided by 1.732 (correction factor for 3 phase) = 25! .84 Volts which is 5.3833%.


It requires that you double the distance and concludes that # 10 will give 5.8 %

loss of power due resistance in the wire.


This only takes in to account the DC resistance; this does no factor in impeadence which is dependent on the frequency. As this is wild AC this will vary somewhat but this is still a factor that has to be considered sue to the length of the run.


Like wise a # 8 wire has a resistance of 2.551 ohms/1000' and this comes to 3.7 % loss.

_
___________________________


I have had it presented another way which concludes with a #4 wire. Can anyone give me some verification of this method and/or suggestions related to it? Also any opinions about what level of loss to accept?


Thanks so much,


Mike d

« Last Edit: January 12, 2006, 02:46:06 AM by (unknown) »

hydrosun

  • Sr. Member
  • ****
  • Posts: 399
Re: Wire sizing for Western North Carolina hydro p
« Reply #1 on: January 11, 2006, 08:09:55 PM »
I always thought 10 guage wire had 1 ohm per 1000 feet. So for 4400 feet you get. 4.4 ohms times 2.5 amps gives 11 volts drop. Someplace along the line you multiplied twice. I not familiar with the three phase factor but I'll take your word and divide by 1.73 and get a drop of 6.5 volts for a loss of less than 1 1/2 percent. You could probably even go with a 12 guage wire with less than 3 % loss. With hydro it's not as critical  to keep the line losses under 2% like solar. With solar you have a limited voltage  window, especially on hot days. With hydro you usually  have a surplus of power and can afford to lose alittle more.

Chris
« Last Edit: January 11, 2006, 08:09:55 PM by hydrosun »

wooferhound

  • SuperHero Member
  • ******
  • Posts: 2288
  • Country: us
  • Huntsville Alabama U.S.A.
    • Woofer Hound Sound & Lighting Rentals
Re: Wire sizing for Western North Carolina hydro p
« Reply #2 on: January 11, 2006, 08:42:04 PM »
This may help you out a lot . . .


Voltage drop calculator:

http://www.electrician.com/vd_calculator.html

« Last Edit: January 11, 2006, 08:42:04 PM by wooferhound »

willib

  • SuperHero Member
  • ******
  • Posts: 2414
  • Country: us
Re: Wire sizing for Western North Carolina
« Reply #3 on: January 11, 2006, 09:03:34 PM »
thanks woofer.

it looks like #3 gage will give you about a 4 percent loss given

480V three phase  @ 18 A , and 2200 ft. run of wire..

sounds like an interesting project !

got any more details?
« Last Edit: January 11, 2006, 09:03:34 PM by willib »
Carpe Ventum (Seize the Wind)

RP

  • Hero Member
  • *****
  • Posts: 722
  • A dog with novelty teeth. What could go wrong?
Re: Wire sizing
« Reply #4 on: January 11, 2006, 09:12:28 PM »
As long as neither of these is a typo, 480V at 1200 watts is less than 3 amps and that's for single phase.  You could probably run this through monster speaker cable with minimal loss.
« Last Edit: January 11, 2006, 09:12:28 PM by RP »

drdongle

  • Hero Member
  • *****
  • Posts: 552
Western North Carolina hydro project
« Reply #5 on: January 11, 2006, 09:17:14 PM »
Where in West NC, Pyrocast is near Hendersonville and I am near Newport Tn.
« Last Edit: January 11, 2006, 09:17:14 PM by drdongle »

willib

  • SuperHero Member
  • ******
  • Posts: 2414
  • Country: us
Re: Wire sizing
« Reply #6 on: January 11, 2006, 09:22:17 PM »
Hmmm i took his 18A figure as his load .
« Last Edit: January 11, 2006, 09:22:17 PM by willib »
Carpe Ventum (Seize the Wind)

mojisimo

  • Newbie
  • *
  • Posts: 10
Re: Wire sizing
« Reply #7 on: January 13, 2006, 06:01:44 AM »
I am putting a micro hydro system in at Turtle Island and am learning about wire sizing.


It is less than 3 amps but the 1200w machine @ 480 volts produces 3-phase power. It is the hi induction power high voltage version of the Harris Hydro machine.


On the calculator suggested by woof it requests "load in amperes", I assume that is the amps from the machine ~2.5 (1200w and 480 volts). Doesn't really sound like a "load" to me, but I am in the learning process . . .


I really am trying to find some info on the math behind the calculation. I am teaching a class about microhydro and would like to have a well-advised process for determining this value. I understand to use the ohms per 1000' feet value to determine # of ohm's based on distance (mine is 2200 ft). But I was advised by an electrician to double that distance. Then multiply the ohms lost by the amps (~2.5) to get voltage drop. At this point I have been advised to divide by a correction factor for 3 phase of 1.732 for the final voltage drop. Then calculate the % of total voltage.


If someone (an electrician hopefully) could verify the doubling of the distance and also the correction factor and maybe a short description of why to do each of these things I would be greatfull.


Thanks,


Mike d

« Last Edit: January 13, 2006, 06:01:44 AM by mojisimo »

drdongle

  • Hero Member
  • *****
  • Posts: 552
Re: Wire sizing
« Reply #8 on: January 13, 2006, 06:16:24 AM »
Where is Turtle Island?
« Last Edit: January 13, 2006, 06:16:24 AM by drdongle »

ghurd

  • Super Hero Member Plus
  • *******
  • Posts: 8059
Re: Wire sizing
« Reply #9 on: January 13, 2006, 06:25:56 AM »
Double the distance because the wire and the amps go out and back.  Many wire charts have the 'round trip' distance figured in.

G-
« Last Edit: January 13, 2006, 06:25:56 AM by ghurd »
www.ghurd.info<<<-----Information on my Controller

mojisimo

  • Newbie
  • *
  • Posts: 10
Re: Western North Carolina hydro project
« Reply #10 on: January 13, 2006, 01:50:20 PM »
Boone, NC


Turle Island is a very neat place, you can learn about it at tutleislandperserve.com.

« Last Edit: January 13, 2006, 01:50:20 PM by mojisimo »

mojisimo

  • Newbie
  • *
  • Posts: 10
Re: Wire sizing
« Reply #11 on: January 13, 2006, 01:52:31 PM »
This is true for 3 phase? Round trip and back, what about the division factor for 3 phase power?
« Last Edit: January 13, 2006, 01:52:31 PM by mojisimo »

drdongle

  • Hero Member
  • *****
  • Posts: 552
Re: Western North Carolina hydro project
« Reply #12 on: January 15, 2006, 01:15:00 PM »
Boone isnt so far, I go to Grandfather mtn every year and it's only a few miles farther out.
« Last Edit: January 15, 2006, 01:15:00 PM by drdongle »

scottsAI

  • Hero Member
  • *****
  • Posts: 884
Re: Wire sizing
« Reply #13 on: January 16, 2006, 10:43:22 PM »
NO.

Use the link to the calculator. They know what there doing.

Play with it, try single phase then 3 phase. The line losses changes a lot.

For a given cross sectional area, you can send more power with 3 phase than single.

The difference is not huge, but significant. That is why the utility's use 3 phase.

Have fun,

Scott.