NICE display indeed.
There several ways how to make the 150 amps shunt.
You get 3 each 50 amps, 50 mv shunts and place them in parallel VOILA 150 amps shunt.
Also 1 each 100 amps with 50 amps, 50 mv shunts in parallel: VOILA 150 Amps shunt.
In either case you only read one 50 amps shunt or even you may parallel the readings point with equal wire lengths.
Also one can use a shunt, let's say 100 amps and with some other known calibrated ammeter in series, you generate certain, let's say 75 amps and you add a resistor in series with the ammeter leads until it reads 50 amps, there you have the display set for 150 amps, ( the shunt will be able to carry the 50 additional amps).
Again if interested let me know to give the steps necessary to attain such job.
To make an accurate shunt you need precision equipment and and alloy that has zero temp coefficient.
If you really are going to get the shunts and need to know how to parallel them, let me know.
You do not need to change the display, one can apply a multiplier factor like 1/2
to what the display say.
Nando