GNB Battery bank question
« on: January 30, 2007, 09:04:12 PM »
I just bought an old forklift 24v battery bank. age is unknown.

It's 12 2V cells wired in 24V but i split it into 2 banks of 12.


the one bank seems ok nut when charging the second bank(it was 10V when i got it)

it didnt want the charge and tool no amps.. then a while later it accepted 12a but then one of the 2volt cells began puffing smoke bubbles. most likely an internal short.


My question is this, since i have no more cells to replace the shorting one can i keep it on charge and perhaps the short will burn away and maybe brink the pack back up or will it just blow a 20ft hole in my wall??


anyone had similar trouble? suggestions?  know get a new bank but i would like to save this one if possible.


thanks


jamie

« Last Edit: January 30, 2007, 09:04:12 PM by (unknown) »

whatsnext

  • Sr. Member
  • ****
  • Posts: 449
Re: GNB Battery bank question
« Reply #1 on: January 30, 2007, 03:12:54 PM »
How are your fluid levels and Specific Gravity of each cell?
« Last Edit: January 30, 2007, 03:12:54 PM by whatsnext »

solarengineer

  • Full Member
  • ***
  • Posts: 136
Re: GNB Battery bank question
« Reply #2 on: January 30, 2007, 04:08:46 PM »
fluid levels are above the plates. sg i havent checked yet since i was giving it a quick charge first. for about 24 hrs.
« Last Edit: January 30, 2007, 04:08:46 PM by solarengineer »

RogerAS

  • Sr. Member
  • ****
  • Posts: 329
Re: GNB Battery bank question
« Reply #3 on: January 30, 2007, 04:13:06 PM »
Jamie,


Saving the one cell may be possible with a desulphator or an electrolyte change.


ELECTROLYTE CHANGE: You could isolate it, the bad cell, from all other cells and try a complete flushing and replacement of the acid. A turkey baster with a small straw that will reach the cell floor might help here. Actually I'm not so sure I would do this myself but it is theoretically posible. Drain all acid very carefully into an approved container. Refill with pure distilled water, apply a small current ( 1 to 2 amps ) to just this cell for several hours, and drain this. Repeat until water drained is clear with no sediment or debris. Refill with fresh new acid as per cell specs. Charge again with small current for several hours and take specific gravity readings before during and after a good long slow charge cycle. Early in this stage of recharging note the cells physical response as well. If the smokey bubbling persists the cell may be shorted beyond help. Stop immediately any such further activity with this cell! (see below for why).


DESULPHATORS: Electronic pulse width modualtion and other methods have been devised to desulphate a battery. Sometimes these can "vibrate" the cause of a shorted cell apart with high intensity current spikes, some using higher voltage as well. I feel these work better in cases where the sulphate hasn't already shorted a plate. In combination with a flush out, however, this may save the cell.


USE CAUTION: Wet cell batteries can explode violently when a dead short occurs between plates. I have had it happen to my car. My '65 Mustang blew its battery sky high right in the service bay of an automitive electrical shop. I'd been having low battery problems for a couple weeks when I took it in. While the engine was running the tech loaded the battery with a resistive pile and she went KABOOM all over the man's shop and the inside of my engine compartment. He had a large bucket of soda water standing by and said it happened more often than he's cared to talk about. A lot of fersh water later and a new battery put the 'Stang back on the road. Acid and flying shrapnel are not so much fun.


REPLACE ONE CELL: Somehow find a replacement of the one bad cell. Even a new cell would save the second half of the 12V system. Sure there would be imbalance and other issues but it would work to get some life out of the other cells. Before doing this consider wether the second half of the 12V string is worth trying to find a very similar cell to make up that second string. A single cell of twice the capacity but still 2V would replace one bad cell and one used but working cell.


LAST DITCH SOLUTION Connect 5 sets of your 2V cells together in parallel then complete the 12V string with  one "stand alone" cell. Rotate a new cell into the "stand alone" position often. Keep a record of the charging/discharging cycles and give them a good slow equlization to start off their new life. The bank capacity will be the capacity(IN AMP HOURS) of the one "stand alone" cell, but if voltage is kept fairly high this should work, but not well. Charging rate would have to match a one cell rate, amperage wise.


I'm not suggesting you do any of these things but they are you options and I'm sure others will add more informed advice.


Below is a small pulser circuit I designed to desulphate via PWM. Load is the battery in this application. The 18V zenner was used as a safety trip to activate the FET when powered from a small windturbine and wouldn't be needed in a steady state source. This design is for a complete 12V system and would have to be modified for 2V operation, or pulse the 2V cell with the 12V source. C1 and C2 are not listed for uF value and experimentation is required for ferquency and duration of the pulse width. A 10uF @ C1 should work fine, and a 4.7uF for C2.




« Last Edit: January 30, 2007, 04:13:06 PM by RogerAS »

solarengineer

  • Full Member
  • ***
  • Posts: 136
Re: GNB Battery bank question
« Reply #4 on: January 30, 2007, 05:47:55 PM »
Thanks for the detailed post Roger!! i will try the desulfator


thanks

« Last Edit: January 30, 2007, 05:47:55 PM by solarengineer »

whatsnext

  • Sr. Member
  • ****
  • Posts: 449
Re: GNB Battery bank question
« Reply #5 on: January 30, 2007, 07:36:08 PM »
I would have checked the voltage and SpG first before a quick charge but that's just me. If your cell was really 'shorted' it would do nothing and the other cells would boil over. Based on an utter lack of info my best guess is sulfation.
« Last Edit: January 30, 2007, 07:36:08 PM by whatsnext »

Gordy

  • Full Member
  • ***
  • Posts: 151
Re: GNB Battery bank question
« Reply #6 on: January 31, 2007, 03:04:48 AM »
If it turns out to be a shorted cell that the desulfator won't fix, You can take the battery apart to clean and fix it. Unless the plates are rotted out.


One of my dad's neighbors in AZ makes his retirment income rejuvinating and rebuilding batteries. He told me to take the top off, you need a trigger type soldering gun witha flat knife like tip. Locate the assembly seam near the top and get the tip hot, insert the hot tip in the seam to melt the plastic. Work your way around the battery till the top comes loose. Lift the top and guts out of the case. nd rinse off with a garden hose. Now you can use a putty knife or whatever will fit between the plates to remove sulphates, an inspect for worped plates. These can be straightend. Using a clean plastic pail and an old T shirt strain the sulphates out of the electrolite, and clean out the battery case.


Reassemble the battery, To reseal the batery case use a V shaped tip in your soldering gun to melt/weld the case back together. A coffee can lid cut into 1/4" strips or simular plastic will be needed for filler. I have done this to repair a battery that was droped and cracked, and another that got to close to an exaust pipe and had a quarter size hole melted in the top.


Put the electrolite back in and charge. If the specific gravity does not come up to the proper level, you'll have to drian the battery and use new electrolite.


You will want to use old cloths, safty glasses and or full face sheild, rubber gloves, make a full length apron from plastic and light rope, ect. Also keep handy an open box of baking soda and water, just in case.


Good Luck,

Gordy