Hi MartyM
I'm guessing that this question pertains to what Flux mentioned about the power factor correction caps causing problems if the grid goes down, and Nando's reference to it elsewhere.
I'm guessing this post did not appear where you expected. If these guesses are correct then
"How will this adjustment in power factor affect my desire to turn the meter backwards.
A) Makes my electric meter register less power then I actually provided to the utility company (bad for me).
B) Makes my electric meter register more power then I actually provided to the utility company (good for me).
C) No change, the meter registers exactly the same amount of KWH transfer in both directions."
Answer A
As power factor moves away from unity, the current you have managed to generate out of phase with the voltage will not register at the meter. This out of phase current still needs to be generated. A vector of the current at the phase angle will show the new in phase current
The watthour meter only sees the inphase amps x Voltage. The further the Power Factor moves away from unity, the more the difference between power into the generator, to useable in phase power out will be.
We can use Caps on the output to correct for this, but the anti-payoff comes when the grid goes down. Then the caps will provide the exciter field and the induction motor will continue to generate. At this point without load, it can (depending on capacitance and load) generate quite high voltages and currents, which if still hooked up to anything in the house, could be detremental to their health.
Why the phase variance with increased power? Flux or Nando may be best for this. I think it has to do with reactance through restive inductors. This gets worse as current goes up, slippage goes up, and resistance drops voltage through the inductor, and so things get a little out of whack..... but I could well be wrong here.
..........oztules