I am not sure how relevant wind data from 60 miles away is. Local factors could make it drastically different.
You are not likely to change Betz limit, I am not sure if your 20% is 20% of Betz or a Cp of 20%. You are not likely to achieve a Cp of more than 20% over much of the range.
Even so your figure seems high.
I tried 11 mph into Michael Klemen's table for a good turbine, which is better than anything you are likely to get.
11mph is 2.67 kWH per month per square foot. 10 ft dia is 78.5 sq ft.
giving 209.6 kWH per month. Per year you have 2515 kWH. Assuming the standard measuring height is 30 ft and you are working at 75 ft you will do better, but as the figures are optimistically high to start with, probably not much better.
Local wind conditions could throw this way out. If your life depends on it you should have done 5 years of wind survey at your site.
Michael Klemen's figures are based on a Rayleigh distribution, you may not have that but you will never know without extensive measurement.
Flux