My pocket reference shows:
(22AWG 25.3 mil dia.) at .019 Ohms/foot @ 149 deg F.
(14AWG 64 mil dia.) at .00297 Ohms/foot @ 149 deg F.
A quick rule of thumb is any time you double up a wire, this reduces its wire gauge by 3. So a pair of 22 AWG wires is approximatly equal to a 19AWG wire.
A more accurate way of doing this is to add up the circular mils of the wires in parallel. For example the 22AWG wire has an area of 642 circular mils, two of them in parallel have an area of 1284 circular mils which is about equal to a 19AWG wire with an area of 1290 circular mils.
To equal a 14AWG wire (4110 circular mils), you would need 4110/642= 6.4 or say 7 22AWG wires in parallel.