Wpowokal is right..how long will they spend at that voltage..
I have found with my 650amp/ L16 battery bank and my 2volt 600amp/hr wet cell battries that they need to reach and hold 28 volts for a couple of hours before they are fully charged to the hydrometer and trimetric meter.
30 volts for equalizing until each battery is 6.5 volts.
But my batteries rarely get to float stage because they are constantly in use.
My TS 60 is set for the L16 setting as a dump load controller.
MX60 is set to hit 28 volts for a absorbtion stage
When using the genset for extended periods (like 30 days ) 26 volts for float.