It's very simple. If the breaker says that it's useable for AC, use it for AC. If it says DC, use it for DC. If it only says AC, don't use for DC. And reverse.
AC (50/60Hz) goes through zero 100 times per second, so the arc that starts when opening the breaker or switch gets extinguished. In DC, the arc can continue to exist for much longer, causing damage to the breaker/switch.
I only use breakers/switches that have a KEMA-keur (or VDE); like your Underwriter's Laboratory (UL). And only use for the way the manufacturer specifies. I.e. no tricks, capacitors, etc.
Many switches can be used for AC and DC, but usually the ratings for DC are much lower. Because of the arc that occurs and doesn't get automatically extinguished.
Hope this is of help, Stephen.
But I don't suppose Trizzybob understands all this. Oops, I meant 2windy.
Peter.