Everyone, I will try my best to supply as much information as I have for this question. I have searched the board and haven't found a post that really answers this for me. This question is mainly because I can't find good information for the forklift battery I have yet. In the Xantrex Prosine 2.0 inverter, I have to set up the charger using custom settings since my battery is not one listed in it's internal charts for charging. Being new to all this I don't quite understand all the settings. What I need to know is your recommendation for the various settings for Bulk, Absorption, Float, Overcharge and Equalize. I have included text from the manual as well. First, the battery: GNB 24V 750Ah Forklift battery converted to 12V 1500Ah. The SG on this battery has always been low: 1.250 after charging at 15A for several days. But, I was using a car charger. I only got two charge cycles on the battery with the previous inverter before it failed and it wasn't set right either. All cells SG is equal, all cell voltages are equal while charging or just sitting. I don't have enough free energy yet to properly charge this battery so for now, I will be using the Prosine's charger to: one, to charge it up and two, to try to desulfate it since the SG is low even after charging it once or twice with the inverter charger. This week, I finally made contact with a gentleman named John from
http://www.arconequipment.com that took the time to give me some numbers for the battery. He was pulling the info he gave me out of his head but assured me he knew forklift batteries well. He said run a couple of equalize charges on it with as much as the charger will put out, watching the SG to see if it comes up a little each time, run it down to 80% then regular charge the battery with as much as the charger will put out (Prosine is rated for 100A but I don't want to run it at max right now, I just replaced it, the previous unit lasted two weeks and blew. So, I'm thinking around 80A) until the voltage per cell reaches 2.37 X 6 = 14.22 then allow it to go into absorption mode. While in absorption mode, hold that voltage and allow the current to drop down to around 30A then go into float mode. He said then to go about three hours more while floating. So, Here are the available settings as they appear in the menus of the inverter and below them are the manual's explanation of what each setting is. I know it's a long post, if a question like this is too much to ask then it's ok by me to delete this post. If I knew more information about my battery I would just call Xantrex. Also, in the battery setup, there is one more setting I don't know what to set, it is: Battery temperature coefficient. It's currently on -15.00mV/Fahrenheit it has a fairly fine setting for the values. Any help for these settings would be greatly appreciated. The following settings are as they appear on the inverter menus. The prosine's manual is in my files section.
Kelly
Bulk Charge Settings:
Max Voltage = I don't know what to set this to compared to the Threshold Voltage
Max Current = %C 5% = 75 A 10%=150A Since my battery is 1500 AH and the Inverter maxes at 100 A I am going to set this a bit lower for now so it don't fry again. I was also thinking of lowering the setting for the Battery Ah so the percentages could be tweaked better, what do you think?
Threshold Timeout = 3min Default, I understand this setting as how long before the battery switches modes
Threshold Voltage = 14.2 I set this myself according to what John said
Absorption Charge Settings
Max Voltage = I don't know what to set this to.
Max Current = %C 5% = 75 A 10%=150A The percentage of the Max Current goes from 5-10% with nothing in between.
Max Timeout = 12 hours Default, I understand this setting as how long before the battery switches modes
Threshold Current = 2% = 30A I set this myself. This percentage can be set with .1 divisions
Threshold Timeout = 3min Default, I understand this setting as how long before the battery switches modes
Overcharge Mode Settings - I don't understand what the difference is between this and Equalize
Max Voltage = I set this to 14.6 but not sure what to set it to.
Max Current = %C 5% I set this
Max Timeout = 0min Default, Not sure about this
Float Charge Settings
Max Voltage = 13.8 Default, this might be close?
Max Current = %C 5% = 75A I set this, again to keep the inverter from hitting 100A
Max Timeout = 21 Days Default I guess the charger will shut down after this?
Threshold Voltage = 12.5 Default when voltage drops below this, goes back to bulk mode.
Threshold Timeout = 15min Default When Voltage drops and remains for this time, goes to bulk mode.
Equalize Charge Settings
Max Voltage = 16.5 I set this according to an average of the other presets in the inverter tables
Max Current = %C 10% I set this, will max out the charge rate to 100%
Max Timeout = 4 hours, I set this, not sure
Threshold Change: 0.0v Default
Threshold Timeout 0min Default
From the Manual:
Bulk Charge Mode Settings
Max Voltage
This is the maximum available charging voltage for the Bulk charging stage.
Max Current (%C)
The maximum available charging current (in A) as a percentage of battery
capacity (in Ah) for the Bulk charging stage.
Threshold Voltage and Timeout
When the battery voltage goes above this value for the Threshold Timeout
specified, the unit goes into Absorption charging stage.
Absorption Mode Settings
Max Voltage
This is the maximum charging voltage for the Absorption charging stage.
Typically, the battery will be at this voltage for the duration of this stage.
Max Current (%C)
The maximum available charging current (in A) as a percentage of battery
capacity (in Ah) for the Absorption charging stage.
Max Timeout
This is the maximum amount of time that the unit will stay in the Absorption
stage.
Threshold Current (%C) and Timeout
When battery current goes below this value (A as % of battery capacity in Ah)
for the Threshold Timeout, the unit goes into the next charging stage.
Overcharge Mode Settings
Max Voltage
This is the maximum charging voltage for the Overcharge charging stage.
Typically the battery will be at this voltage for the duration of this stage.
Max Current (%C)
The maximum available charging current (in A) as a percentage of battery
capacity (in Ah) for the Overcharge charging stage.
Max Timeout
The amount of time that the Overcharge stage will run.
Float Mode Settings
Max Voltage
This is the maximum available charging voltage for the Float charging stage.
Typically the battery will be at this voltage for the duration of this stage.
Max Current (%C)
The maximum available charging current (in A) as a percentage of battery
capacity (in Ah) for the Float charging stage.
Max Timeout
This is the maximum amount of time that the charger will be in Float stage.
Threshold Voltage and Timeout
When the battery voltage goes below this value for the Threshold Timeout
specified, the unit goes into Bulk charging mode.
Equalize Mode Settings
Max Voltage
This is the maximum available charging voltage for the Equalize charging
stage.
Max Current (%C)
This is the maximum available charging current (in A) as % of battery
capacity in (Ah) for the Equalize charging stage.
Max Timeout
This is the maximum amount of time that the unit will stay in Equalize stage.
Threshold Change and Timeout
When the battery voltage changes by less than the change value over the
Threshold Timeout specified, the unit goes to Float charging.