OK Hugh, I'll byte... (just a little byte though)
A lot of people have hooked up MX60s to wind turbines, even without being "wind ready"
I'm not exactly sure WHY they sometimes work, but it ~might~ be because they happen to have a steady flow of wind instead of lots of ups and downs or something like that.
Yes, you can hook a solar array in parallel with a (small-ish) turbine, where the PV array "clips" the voltage at just above the temperature dependent Voc Voltage during battery full (etc) times... This works either day or night. This can work fine as long as you are certain to add the PV manufacturers specified series fuse to the series PV string. So, the PV array MUST be able to handle the maximum current the turbine can put out at that voltage. The turbine current cannot go above that series rating. Hopefully it's somewhat less than that to avoid nuisance breaker/fuse tripping. This clipping method also works well in small hydro hookups.
If the turbine and array are capable of about the same amount of power at the same voltage, then all is fine, as is with the old MX MPPT algorithm. But if the MX somehow finds the MPP Voltage of the turbine to be higher than the MPP V of the PV, then when the wind dies down, the MPP V will stay high until the MX sweeps again. This also means that the MX could possible see low power for a minute or two (or...) and might go to sleep and wake back up to do an initial sweep. So you would want to be aware of behavior like this.
The newer MF60 and MF80 should most likely work better than the MX in this type of hookup because when the power starts to go up with the wind speed, so should the input voltage of the MF. And when the wind dies down, the PV input voltage should come down again (i.e. dynamic tracking.)
Also, if you do use a PV array to clip the wind turbine voltage, use some PV voltage below 72V nominal to make sure it doesn't go above 150 Volts. Wire the PV array to have its MPP Voltage somewhat higher than the nominal voltage (12,24,48V) of the turbine I would say, because typically the cutin voltage of the turbine is going to be around the battery voltage and you want it to run slightly higher than the battery voltage to take advantage of all this. For instance, for a 12V battery system, I'd try starting with a 24V nominal wired PV array with either a 12V or 24V nominal wound turbine, where the MPPV is around 33 Volts. You won't get any power out of the turbine until its voltage reaches at that 33 Volts (at least) but that's OK because open circuited, the turbine would probably have been higher than that anyway.
>>>I use a shorting switch to stop my units.
You will not want to short the PV input while the MX/MF is running though. Make sure you disconnect the MX before connecting the short across the turbine and/or array. The MX and most all MPPT controllers do have a few thousand microFarads of capacitance across their inputs already.
OR, you may just want to wait for a proper controller to come along first (MX or Classic) and use the MX60s built in diversion Aux output control temporarily.
If you're careful, it's a lot of fun to see this stuff work.
boB