when i`m calculating what the max panels i can put on a a fronius IG30


is it the max open cct voltage or the "working" voltage of the panels that must be considered..


using sharp 180watt NUS0E3E panels

fromius has 1 input string (1 mpp)


Thanks,

Richard

« Last Edit: February 04, 2009, 08:45:02 PM by (unknown) »

electronbaby

  • Sr. Member
  • ****
  • Posts: 407
  • Country: us
    • Windsine.org
Re: grid tie inverter voltage fronius IG30
« Reply #1 on: February 04, 2009, 03:15:10 PM »
Use the max open circuit voltage of the PV string. You need to know the temperature coefficient of the cells and modules. If you use a string sizing guide, this is taken into account. It will ask you for your record low temperature in the area you are installing. This can be found at any weather site usually (like the Weather Channel). This is because the PV string VOC goes to its highest level during cold temperatures. It also decreases when the modules heat up. However, no damage is done when the string voltage falls below the inverter operating window. Damage could occur if the string voltage exceeds the safe limits of the inverter equipment.
« Last Edit: February 04, 2009, 03:15:10 PM by (unknown) »
Have Fun!!!  RoyR KB2UHF

dnix71

  • SuperHero Member
  • ******
  • Posts: 2513
Re: grid tie inverter voltage fronius IG30
« Reply #2 on: February 04, 2009, 08:29:16 PM »
The spec sheet says 500v. Even dc, I don't think I would want to go anywhere near that high. Those things paramedics use to restart hearts only use 400v dc. The Voc for those panels is listed at 30. 10 in series would be a safe number.


http://www.energymatters.com.au/fronius-2650watt-grid-connect-inverter-ig30-outdoor-ip45-p-621.html




« Last Edit: February 04, 2009, 08:29:16 PM by (unknown) »

dnix71

  • SuperHero Member
  • ******
  • Posts: 2513
Re: grid tie inverter voltage fronius IG30
« Reply #3 on: February 04, 2009, 08:31:21 PM »
The panels specs are:

« Last Edit: February 04, 2009, 08:31:21 PM by (unknown) »

rgormley

  • Newbie
  • *
  • Posts: 33
Re: grid tie inverter voltage fronius IG30
« Reply #4 on: February 05, 2009, 02:38:59 AM »
best i dont touch the system i`m getting installed then as it will be 11 x 30 volts!! (330)


hhhmmm that is a very lethal combo!!


and i thought i was scared of 240 AC!

« Last Edit: February 05, 2009, 02:38:59 AM by (unknown) »

electronbaby

  • Sr. Member
  • ****
  • Posts: 407
  • Country: us
    • Windsine.org
Re: grid tie inverter voltage fronius IG30
« Reply #5 on: February 05, 2009, 09:18:06 AM »


« Last Edit: February 05, 2009, 09:18:06 AM by (unknown) »
Have Fun!!!  RoyR KB2UHF

TomW

  • Super Hero Member Plus
  • *******
  • Posts: 5130
  • Country: us
Re: grid tie inverter voltage fronius IG30
« Reply #6 on: February 05, 2009, 09:37:23 AM »
Roy;


Thats an awful expensive ion generator you got there. Or is it just a welder?


Haha Excellent graphic example of how High Voltage DC can behave.


Tom

« Last Edit: February 05, 2009, 09:37:23 AM by (unknown) »

electronbaby

  • Sr. Member
  • ****
  • Posts: 407
  • Country: us
    • Windsine.org
Re: grid tie inverter voltage fronius IG30
« Reply #7 on: February 05, 2009, 12:08:02 PM »
HA thanks. This arc was pulled off this array pictured below. I did this system a while back. Its 10kw Amorphous Commercial system. It was not particularly sunny at play time either....Otherwise I would have had to watch my feet for molten copper. Dont try this at home. :-)



« Last Edit: February 05, 2009, 12:08:02 PM by (unknown) »
Have Fun!!!  RoyR KB2UHF