Tending to agree with all of this with one addition -
I generally don't like automatic low end cutoff (particularly if I can't easily adjust the threshold) because of all the discrepancies that pop up under different circumstances. Discharging a battery with 60% SOC with heavy load and a light drain on a battery that is actually discharged can appear very similar... there's really no [practical] way to see the difference electronically, unless you want to develop some kind of crazy sensing array that measures all kinds of things and makes an 'intelligent' decision. It would be more expensive than it was worth IMHO.
As Flux pointed out, its good for a last resort if you're not available to intervene manually, but isn't really good for everyday limiting.
I prefer an alarm (with ability to mute of course) to let me know that terminal voltage is out of bounds, and that lets me decide if this is a normal condition for what is going on or not.
If I'm sucking 100A from a 200AH battery with a decent charge on it, I would still expect it to be pulling down a bit, and so it's not really an issue at that time, and I would mute the alarm.
If I'm pulling 1A from the same battery, and the alarm is going off, it's dead and I need to do something else for juice before I damage it.
If I continue to ignore the alarm status, and voltage dips below 9, then I should be considered an idiot (just as if I had not payed the electric bill), and power should be automatically disconnected until I resolve the problem.
Yes?