Hi sbotsford,
You mention that you have grid power, what you have not told us is if your system is battery based (with an inverter), and you're looking to charge batteries with that 7kW wind turbine. Alternatively, you don't have any inverter yet, and are looking for net-metering, so all you need is a grid-tie inverter for the wind turbine.
In the latter case, I would suggest either a Power-One Aurora wind inverter (they can safely be programmed up to 6.2kW of output power), or an SMA Windyboy. Keep in mind that both need to be programmed with MPPT information for your specific wind turbine to work properly. They do *not* work out of the box. Both have an absolute maximum voltage of 600V DC, and I make good money selling Aurora inverters to people that blow them up by going overvoltage. That is the one guaranteed way to let the magic smoke out, and warranty does not cover it. In other words, you have to make sure your turbine can not produce more than 600V DC (there are several ways to do this).
Even with overvoltage protection I would not get anywhere near 600V DC for normal operation, you need a buffer to protect the inverter in case things go wrong. A good voltage to shoot for is 400V DC, maybe 450V (as a maximum). At 400V DC you're looking at 15.5A for 6.2kW. For 2% losses at 400 meters that works out to 0.52 Ohm total, or 0.26 Ohm for each leg. That means 1 AWG aluminum wire (nobody uses copper for those distances, just too expensive). about a thousand dollars will do that, for underground service entrance rated wire that can be dropped directly into the ground. Less if you're willing to go for somewhat higher peak losses, which has almost no effect on total energy production for a wind turbine since so little time is spent at peak power.
On the total cost of a 6 or 7kW wind turbine, inverter, tower and everything else, the cable cost is a small portion when going with the voltages above (400V DC or so). No point in shooting for 1kV or more, there's very little to be saved and you can't get inverters for it. Nothing off-the-shelve that's UL/CSA listed in any case.
By the way, I used DC voltage above, putting the rectifier near the turbine. You can also go with 3-phase AC voltage over the wires, for 400V DC that works out to about 300V AC phase-to-phase. It will cost just about the same in cable though (3-phase current will be less, you can probably go a gauge smaller, but now need 3 conductors instead of 2).
-RoB-