I got wind, solar and standby gen, although our standby gen for the house and shop is LP fueled (6 kW Generac EcoGen).
The inverter controls the generator with a box called a "GSM" (Generator Start Module) that looks like this:
The inverter has pretty elaborate generator controlling schemes in its programming that prevents it from starting the generator unless it's absolutely necessary. There's a series of timers and monitoring systems in there starting with (all these generator control parameters are programmable for what you want them to do):
- a 24 hour timer that monitors bank voltage and if it drops below 25.0 for more than 24 hours that means there hasn't been sufficient RE power to fully charge the batteries. So the inverter starts the gen and does a maintenance bulk and absorb charge on the bank, then shuts it off. That's usually a very short run time - around 30-45 minutes or so.
- a 2 hour timer that monitors bank voltage and if it drops below 24.0 for two hours it brings the gen online and does a full bulk and absorption charge on the bank, then cools the gen down and shuts it off. This is as low as I like to see my bank go (2,400 amp-hours), and at 220 amps charging rate from both inverters (I have stacked inverters for 120/240 split phase power) it usually takes about 4.5 hours with the gen at full load and all the power going to the chargers. If there's other loads on in the house or shop so full gen power isn't available for the chargers, it will take longer. The inverter manages that and passes power thru to loads as priority and the chargers as secondary
- a 15 minute timer that brings the gen online if the voltage falls below 23.0 for 15 minutes. All these timers do the same thing - a full bulk and absorb charge, gen cool down, gen shutdown.
- a 15 second timer that initiates the gen starting sequence at LBCO (Low Battery Cut Out). The inverters shut down at 22.0 volts after 15 minutes. The 15 second timer starts the gen at LBCO, warms it up for 30 seconds, then puts Full Dawg on it to get some juice back into the bank.
- Load Management - if the master inverter has 30 amp load on it for more than 2 minutes the inverter starts the gen to help out with the heavy load, runs it for five minutes after the load drops below that set point, cools it down and shuts it off. There is no battery charging when the gen is started because of Load Management.
If the inverter starts the generator for any of the above reasons and there is solar power coming in, the solar just helps out with the battery charging. Both of my solar arrays have Morningstar MPPT controllers and the voltage is regulated at the same setpoints that I have set in the inverters for bulk/absorb/float.
If the inverter starts the generator for any of the above reasons and there is wind power coming in, the wind power is not voltage regulated. So it helps out and the inverter "blends" the incoming wind power with the gen power until the bank charging parameters are reached, then if there's too much wind power for the inverter to "blend" it with the gen power, it "spits the gen off" - unloads it, cools it down, and shuts it off and lets the RE system do its job. The auxiliary loading system then takes over to control bank voltage.
So basically, set up properly, it's a walk away and forget it system. It just takes care of itself. What will screw it up after you have it programmed properly is punching buttons and playing with it. After you have it set up so it "just works" you have to learn to set back in your easy chair and just let it "just work". You only mess with it if the master inverter spits an error warning for something it didn't like, such as "Error O5H: Gen Failed To Start: YES". Then you investigate the problem and correct it (such as, CRIPES! The fuel tank is empty!!!), then walk away and don't mess with it. One of them timers will start the gen if needed after you fix the problem and clear the error.
So that's how it works with my system, and different inverters and generator controllers and whatnot are different. My system is all Xantrex. The wind turbines don't "freewheel" or anything - the inverter just evaluates the situation and takes care of it accordingly.
It's my opinion that automatic generator control is better than a manually started generator. It will save you gen fuel in the long run, and get the best life from your batteries. With manually started backup gen systems the tendency is to pull the bank down too far before starting the gen, and let it run too long after bulk and absorb is done, which wastes fuel and is harder on the bank. If you like to sit around and monitor your power system all the time, then manual if fine. But when we upgraded our system this past summer I set it up so it's fully automatic so I don't have to monitor it. We like to fish and hunt and do other stuff besides sitting around and worrying about whether or not we got enough wind or solar power to carry us thru today.
--
Chris