Is that the same kind of batteries that they use in those computer UPS units?
I've always figured that those things were made to die so you have to replace them all the time.
--
Chris
They are the same batteries used in UPS units.
I think 7AH is more common than 12AH.
The things were NOT designed to die.
The chargers in the UPS units were designed to intentionally kill them.
ie:
Wally Wonker's cash registers need UPS's. The guy in charge of that calls a $150/H guy who knows enough to put an UPS on a cash register. Neither of them know what they are dealing with. In a year when the UPS says the battery is substandard, it is cheaper to BUY A NEW UPS than change the battery, when labor is figured in.
Many UPS makers intentionally make it impossible to know what the DC input voltage is from the data sheets or manuals, because they intend to sell new batteries at 3 to 5X the going rate, or a new UPS.
It is usually cheaper to have new UPSs installed.
And that is why used UPS's with no batteries are cheap or free or thrown in a dumpster.
I have used removed from UPS as 'used and faulty' 7AH 12V SLA for 10 years after the date code, and they still work fine for what I want to do with them.
The trick is to use a decent controller actually suited to them (properly adjusted ghurd controller, VW PV with the built in controller, PB137ACV <137 is 13.7V>, etc?) that will not go past 13.8V.
Don't believe everything you read on a battery charger box. HF crap with coupon box says "13.2V regulated, suitable for 5 to 125AH", but the last maybe 10 I bought go way past 14V.
Below 12.2V is when hard sulfation happens.
If possible, keep SLAs between 13.8V and 12.2V.
I try to keep the 7AH ones in my house between 12.5 and 13.7V. Works for me.
Brian, "robust", yes. As pilots know, that is why they are commonly used in aircraft.