Hi Joe,
The 6kW Aurora wind inverter has an input limit of 36A DC, and it starts working at 50V DC. I suppose that a 17-footer (5.18m diameter) should produce around 4kW by the time you want it to furl (around 11 m/s wind speed), assuming reasonable efficiency. That means you'll need it to reach roughly 120V DC on the input for that to happen (the 36A limit is input current, the 4kW is output power, and there's some loss due to inverter efficiency).
I've helped a few people get their battery-charging turbine grid-tied with Aurora inverters, it can work, but of course this depends a bit on how the turbine was designed. Ideally you want the MPPT curve in the inverter to load up the turbine so it's always running at the best TSR, for the entire range of wind speeds. If your turbine, when coupled to batteries, cuts in late and already runs at a high TSR by the time the wind reaches 11 m/s it will be difficult to get it to produce the higher voltage needed for grid-tie (at least not without grossly overspeeding, which will also make it inefficient). On the other hand, if your turbine is still going slow when on batteries at the higher wind speeds there's hope!
Do you have any means of measuring wind speed, preferably near the turbine on the tower? Any way to measure RPM, so you have some idea of what TSR it's running at? For a 17-footer at 11 m/s and a TSR of 7, it would be doing 280 RPM (or 4.7 revolutions per second). That is fast, probably noisy, likely scary, but for most turbines not a problem. It should be furling just about at that point anyway, to protect itself from higher wind speeds (and RPMs).
Without more information, making an MPPT curve for your turbine is an absolute crap shoot. If you want to try something, try this:
Wind (m/s) RMP DC Volt Watt Out
4 103 50 0
4.5 116 55 280
5 129 60 400
6 155 72 700
7 181 82 1100
8 206 93 1600
9 232 103 2300
10 258 113 3100
11 284 123 4000
This is based on just a single datapoint, which may be completely off for your turbine, of 123 Volt and 4kW out. The RPM is based on a TSR of 7, which may be wrong for your turbine as well, but if you have a way to measure it at least you'll have some idea if the turbine is over/underspeeding vs. wind speed.
In any event, if you post the design TSR of the turbine (where the blades run most efficiently), number of poles of the alternator, unloaded AC voltage (phase-to-phase) vs. RPM, and phase-to-phase resistance, I'll run the number and post an MPPT curve that should be a little more on target. The blade diameter is exactly 17'?
Now, this probably sounds funny since you're having trouble reaching higher voltages, but I see lots of Aurora inverters getting destroyed due to overvoltage. They are very robust inverters, and this is just about the only way to kill them. It's amazing how fast an unloaded turbine can spin up, and once it reaches 600V DC (about 440V phase-to-phase AC), that's the end of the inverter. You have to make absolutely sure that will never happen.
-RoB-