Chris, I follow your logic, but not your math. I'm coming up with 3,125w & 7,031w on the 9.6 ohm resistors at 100VAC & 150 VAC respectively. The 7.2 ohm resistors I'm getting 4,167 & 9,375w. What am I missing?
In delta you have two resistances wired parallel. One phase is always inactive and not conducting. The formula for resistance of parallel circuits is 1/Rt = 1/R1 + 1/R2. For two 7.2 ohm resistors the calculated resistance is
1 / (2 * 0.139) = 3.6 ohm.
While I didn't go thru your math, you might be using three in parallel, which would be:
1 / (3 * 0.139) = 2.4 ohm
The reason you can't use a triple parallel circuit here is because of the way three-phase power conducts and the timing of the phases. Power is being conducted thru any two phases at a time.
Regarding the HyperVOC - read carefully what Chris is saying BRC. The Classic is not destroyed in HyperVOC; it protects itself, but it is not active in the sense of managing the turbine loading in this range. I believe any load into the batteries is gone in this mode. It is solely left to the load bank (and furling).
This is correct. The Classic handles over-volt very well. Because I don't have a prop governor that varies the pitch of the blades I use furling in extreme wind to keep the speed below 450 with a 150V Classic. The machine is producing 185VDC open circuit. But with the "clamp" on the AC side with a three-phase load the over-volt is kept to <160. While the Classic isn't charging the battery at that speed and voltage, the AC clipper is running at full tilt keeping the machine under control (and producing tremendous amounts of power at quite high efficiency).
In over-volt I have 110VAC power @ 75Hz and max 22 amps continuous That is up to 2,400 watts on water heating continuous. It will produce more than that in really high winds, but the duty cycle of the generator is 25 amps for an hour if the outside temp is above about 30 deg F. If it's below freezing so we got good generator cooling it can do 2,500 watts continuous on AC load. But there is spikes where I've seen it send 40 amps to the water heaters before. Obviously, my original clipper could not take this. It got too hot. That's when I came up with why not use this for something useful, that is about 92% efficient electrically from the generator to the load? Water heating.
This can happen on any day when the battery gets to absorb too, even in 10-12 mph wind. The Classic unloads it as the solar takes over and it winds up into HyperVOC running at very high TSR. The AC load comes in and it starts heating water with three-phase power. We don't get no 2.0 kW at 10-12 mph. But it's still VERY efficient electrically, to the load.
It's been running this way for 7 years and I haven't been able to burn up a Classic controller yet. And I'm just using a 150.
When I first started messing with the Classic I tried various engine-driven generators in the shop. This is where I found out the Classic does not like "dirty" power input. It gets really hot if the DC power has ripple from a lot of THD on the AC side of the rectifiers. And the 20-pole high-frequency axial generator design was born. That was actually Les' (Flux) idea. He told me, if you want clean power you need higher AC frequency. Either gear up the 12 pole and run it fast, or put more poles in it. I tried both designs. While the geared design was successful, the 20-pole built to super-accurate specs puts out the cleanest power.