Just a word of caution on this "un-synchronised" transfer....
- Make sure you use "break-before-make" switchgear, otherwise the results can be the release of large amounts of "magic smoke"
- Its not quite as simple as may appear. Mains/grid supply, and your own locally generated supply (unless synchronised, somehow) have no known/fixed phase relationship meaning if you quickly change from one to the other, your sensitive equipment may VERY WELL be destroyed because of the very high "dv/dt" (change in voltage over change in time).
The reason is that lets say at the instant you change from local supply to grid supply, they are 180 degrees out of phase (as is going to be a "common" occurance). Instead of the mains cycle going smoothly and gently from say, -160V (120 RMS has a peak value around 160-170V), to the opposite +160 in the time it takes the relay contacts to change (ie, not long).
I've seen folks use TWO interlocked contactors to do the switching, with a delay between one opening and the other closing - but then your clocks, computers etc are all going to "drop out" when you switch from one to the other.
Of course, the "correct" way is to have your local inverter phase-lock to the grid, but thats a lot more complexity than 99% of inverters provide.