First a few words on what my system is and isn't - it has a bearing on the way I designed the controller(s)!! It is not a system that charges the batteries, dumps the excess and uses the available power as a normal off grid system does but one of charge the batteries and then cream off the top 10% of the charge into one or other of the swimming pool pumps - in effect using the pool pumps (1kw 1HP) as a dump load but never really running the batteries down (except in an emergency).
As a result, the typical voltage charge curve looks like this:
Even though the original controller is charge counting, the voltage gets pretty wild at times and the 1kw load is used in short 10 minute bursts to control the excess.
The new controller I'm working on uses a PWM shunt load to try and avoid the high voltage peaks in the first place but I've been surprised in just how much the voltage is nailed at the shunt cut-in voltage. It is presently set up to start diverting to the shunt at 27 volts with a shunt full on at 28.8 volts with a linear change between. The PWM frequency is about 900Hz (not that that has any effect!)
The shunt is detailed with the rest of the controller at
http://gilks.ath.cx/~g8ecj/New_Turbine/new_controller.html and draws about 25 amps when full on. During the log above is never went over 38%.
Perhaps some of our dear readers have some ideas for the brickwall curve that results!!