Hi there,
When reading your post, something seems wrong. Lets say your average float voltage is around 13.7v, and the charger increases the charging voltage to lets say 16v, the voltage at the batteries is never supposed to instantly jump to over 15v. For example, I have a homemade ~20amp battery charger, that will raise the voltage on a small UPS battery to well over 16v in a matter of seconds. However, when I charge a large 85amp/hour deisel truck battery with it, it puts approx 20amps into the battery, but the voltage at the battery takes quite a long time to move from 12v to 13v. Yet, at the 12v contacts on the charger, the voltage is at that point a little over 14v.
So I have two questions:
- How big is your battery bank because it will take a lot of amps to raise the voltage in a large battery bank to over 15v from a float volage of 13.5?
- Where do you have the inverter connected, at the Charger or at the battery, because due to voltage loss in the connecting wires, the voltage at the charger may be higher than that at the battery bank.
So, if you connect the inverter at the battery bank, the voltage that the inverter reads will take a long time to go over 15v, even if the charging voltage is more than 15v.
Also, if you go over 15v on a battery bank for very long, it can damage the batteries, not to mention the various devices connected to them like inverters. Is this really how the charge controller was designed to work? Mabye you should disable the temperature compensation?