Author Topic: Charging Voltages  (Read 1753 times)

0 Members and 1 Guest are viewing this topic.

geoffd

  • Newbie
  • *
  • Posts: 42
Charging Voltages
« on: December 30, 2004, 10:20:06 AM »
I have a bank of 12 Hoppecke Solar Power 7 Batteries.  These provide 24 volt 1300 Ah at C120.  The bank is charged from an Outback VFX3024 Inverter/Charger fed from a 3kw Generator.


The original spec was to provide 3kw / day for 5 days to a 80 percent discharge.


They don't get anywhere near this, they give about 3kw / day for 2 days, and I think it might be the values I use to charge them.  Currently I have the Boost Charge set to 31.2 volts for 1 hour.


Does anyone know how I can calculate the correct values, there is nothig on this on the Hoppecke website and they have not responded to any of my emails.


Best wishes

Geoff

« Last Edit: December 30, 2004, 10:20:06 AM by (unknown) »

wpowokal

  • Hero Member
  • *****
  • Posts: 1271
  • Country: au
  • Far North Queensland (FNQ) Australia
Re: Charging Voltages
« Reply #1 on: December 30, 2004, 05:23:59 PM »
Geoff,

      While I am not familure with your batteries and checking their site crashes my computer, I did get their sola batteries are flooded lead acid, try reading this.


http://www.trojanbattery.com/customercare_batterymaint9.html

http://www.homepower.com/magazine/downloads.cfm


I run a 24v system and per Kw out of the inverter requires 50A (OK slightly less but for ease of adding), so 3 Kw/day is 150 amps. Therefore 2 days is 23% of battery capacity.


My batteries are flooded lead acid, I use around 32V max. as equalising voltage and maintain that for around 3 hours.


I don't believe 1 hour is adequate, but thats debatable and how often one equalises is also cause for creating an argument however I like to try for once a week but if it's two weeks thats fine also. If the batteries require any topping up from other than Re sources I usually do it weekly and go through to equalisation, thats how I arrive at 1 week intervals.  


Hope this helps

regards Allan

« Last Edit: December 30, 2004, 05:23:59 PM by (unknown) »
A gentleman is man who can disagree without being disagreeable.

Ungrounded Lightning Rod

  • SuperHero Member
  • ******
  • Posts: 2866
Re: Charging Voltages
« Reply #2 on: December 31, 2004, 11:04:17 AM »
The original spec was to provide 3kw / day for 5 days to a 80 percent discharge.


They don't get anywhere near this, they give about 3kw / day for 2 days, and I think it might be the values I use to charge them.  Currently I have the Boost Charge set to 31.2 volts for 1 hour.


That sounds like they need an equalization charge.

« Last Edit: December 31, 2004, 11:04:17 AM by (unknown) »

Nando

  • Hero Member
  • *****
  • Posts: 1058
Re: Charging Voltages
« Reply #3 on: December 31, 2004, 09:03:43 PM »
1300 amphour times 28 volts is 36 KWH


If you are charging 3KW for one hour that is 3KWH.

To attain the 36 KWH charge using a 3 KW generator, you will need a minimum of 36 KWH/3KWH = 12 hours of constant charge plus the additional time needed for the charging efficiency which could go as high as 30 % additional time.


You need equalize periodically but not continually or the bank will not last.

Equalization should be done if a deep discharge has been set on the bank.


Try to keep the charge above 45 % and the equalization will be minimized and maybe done once every 8 charging cycles ( you should have the a good DVM that can read up to millivolts) and keep records, as well as, the electrolyte conditions -- this will allow you to prolong the life of the battery bank.


There are good web sites with detailed battery info.


Regards


Nando

« Last Edit: December 31, 2004, 09:03:43 PM by (unknown) »

geoffd

  • Newbie
  • *
  • Posts: 42
Re: Charging Voltages
« Reply #4 on: January 01, 2005, 06:25:52 AM »
Thanks everyone.


The system is newly installed, but I have not done an equalisation charge yet.  I will give it a go.


Cheers

Geoff

« Last Edit: January 01, 2005, 06:25:52 AM by (unknown) »

troy

  • Full Member
  • ***
  • Posts: 227
Re: Charging Voltages
« Reply #5 on: January 03, 2005, 10:17:10 AM »
Do you have an amphour meter.  This functions as a "gas gauge" for your battery pack.  Using voltage alone as an indication of battery charge gets tricky.  I use voltage plus periodic testing of electrolyte density (battery hygrometer).


Good luck and have fun!


troy

« Last Edit: January 03, 2005, 10:17:10 AM by (unknown) »

geoffd

  • Newbie
  • *
  • Posts: 42
Re: Charging Voltages
« Reply #6 on: January 07, 2005, 12:47:56 PM »
No, the budget does not run to an Amp/Hour Meter yet, but it is on the wish list.


Does anyone have any recommendations as to the most cost effective.


Cheers

Geoff