Welcome to the forum. If you're running 3-phase from the turbine you will need three conductors.
You also didn't mention the voltage of the system. If it is a 12V system, and 1,600w, you're looking at near 90 amps; at 24V it'd be near 46 amps, and at 48V maybe 23 amps. In all but the latter, or if it is MPPT (where the voltage can be higher than the batteries) you will be over the ampacity of the wire.
Usually the size of the wire is determined not by limits of ampacity - #10 ga CU is good for 30 amps - but by the voltage drop over the distance you're going. There are a number of voltage drop calculators on-line (if not on this board), you should try to limit the voltage drop to 2% ideally; and not more than 5%.
Solid or stranded wire will work with DC or AC. Stranded is often used on vehicles as hydrosun mentioned and also on things like welding cables, battery bank wiring, and inverter (DC) wiring mainly because of flexibility, which may be why you're thinking it is associated with DC.
Hope this helps. Good luck, ~kitestrings