I don't recall the size you are contemplating, or if you've determined this Astro. Generally there are two approaches - there are more, but these seem most common - one, is where you are tied to the nominal battery voltage, and you divert, or burn off excessive available power. I think this works well for small to moderate size systems. I think the Tri-star and Xantrex controllers are some of the more common commercial ones used. Gurd, and others have made their own.
The other is to use a MPPT controller, like the Midnite Classic (in Wind Mode), and there are some comparable grid-tied inverters (e.g. Aurora). This is what we have. Here, the input voltage needs a bit of 'headroom' at cut-in, but then can fluctuate much higher than the battery voltage. The controller, bucks the voltage, as it attempts to follow a user-input power curve.
In our case our nominal voltage is 48V. We cut-in at about 58V, and the voltage can go up to 150-160V, but we try to live well below that level (110-120V).
With a direct-tie, I think Hugh recommends shooting for a cut-in of roughly nominal plus 1.4V on a 12V system (2x on 24V, right). I would think wind for something near that mark. The forcing volts will be linear above that point, rising 2-2.5x the cut-in rpm (before helicopter noises commence) and the challenge becomes being able to divert all of the available power from the thing once the batteries are happy, and or start to furl, or otherwise govern.
Hopefully you never run the thing unloaded, or truly open-voltage, as this is where things get hairy in very short order, but I don't think that is what you meant.