ST Generator Head Issue
« on: September 22, 2008, 07:04:05 PM »
I'm still banging my head against the wall with this generator.

I have a Changfa 13 hp diesel engine coupled to a 7.5 KW ST Generator head...


Here are the details...when it is running....



  1.       Hooked up for 220v
  2.       U1 to ground produces 110v
  3.       U2 to ground produces 110v
  4.       U1 to U2 produces 220v (so far so good, eh?!)
  5.       I am still using the stock `doghouse' on the 7.5 kw ST Generator head. U1 and U2 are connected to the bus on a dedicated circuit panel.
  6.       When a load is applied, U1  to ground reads 220v and U2 to ground reads 0! And my kilowatt reads nothing at the outlet connected to the circuit panel.
  7.       When the load is removed, it goes back to the levels in steps 2,3,4


I bought this style set up for it's reliability...the wifey is about to have my head!!


Am I missing something with my setup?

Thanks in advance.

Chuck

« Last Edit: September 22, 2008, 07:04:05 PM by (unknown) »

electronbaby

  • Sr. Member
  • ****
  • Posts: 407
  • Country: us
    • Windsine.org
Re: ST Generator Head Issue
« Reply #1 on: September 22, 2008, 02:08:33 PM »
Is the load using 120v?  or 240?


Check your diodes and caps.

« Last Edit: September 22, 2008, 02:08:33 PM by (unknown) »
Have Fun!!!  RoyR KB2UHF

Ungrounded Lightning Rod

  • SuperHero Member
  • ******
  • Posts: 2865
Re: ST Generator Head Issue
« Reply #2 on: September 22, 2008, 02:56:34 PM »
Try hooking your load between U1 and NEUTRAL, not GROUND.
« Last Edit: September 22, 2008, 02:56:34 PM by (unknown) »

Tritium

  • Hero Member
  • *****
  • Posts: 658
Re: ST Generator Head Issue
« Reply #3 on: September 22, 2008, 02:57:22 PM »
You might want to have a look at this site:


http://www.utterpower.com/ST.htm


Thurmond

« Last Edit: September 22, 2008, 02:57:22 PM by (unknown) »

Ungrounded Lightning Rod

  • SuperHero Member
  • ******
  • Posts: 2865
Re: ST Generator Head Issue
« Reply #4 on: September 22, 2008, 06:25:47 PM »
According to the site Tritium pointed to, Neutral is the jumper between U3 and U4.


Are you using the genny for a 240v load, too, or just 220?  If just 220 you can boost the current by reconnecting the genny so the two output windings are in parallel rather than series.  From the diagrams that's U1&U3 jumpered as one side, U2&U4 jumpered as the other.  But try it by jumpering U1&U3 then checking that you have 120 between that and either of U2 and U4, and only a couple volts between U2&U4, before closing the jumper between U2 and U4.

« Last Edit: September 22, 2008, 06:25:47 PM by (unknown) »

Ungrounded Lightning Rod

  • SuperHero Member
  • ******
  • Posts: 2865
Re: ST Generator Head Issue
« Reply #5 on: September 22, 2008, 06:27:03 PM »
Are you using the genny for a 240v load, too, or just 220?  If just 220 ...


Of course that SHOULD read:


Are you using the genny for a 240v load, too, or just 120?  If just 120 ...

« Last Edit: September 22, 2008, 06:27:03 PM by (unknown) »