Blimey, we're getting it all. Storms, powercuts, pandemics, comms dropping (during powercut 2 hours after because I suspect the reserve batteries are expired) and my keyboard is defective so I haven't been internetting much. I have to open my laptop and reseat the connector every time I want to use a T,P,5,3, u, . , or →...sigh...something to do with Z stacking a ribbon flex I imagine.
Has climate change started already?
Where was I? Ah yes, the widow-maker, AKA suicide lead. It's a lockable three-phase switch Tanner there's no wrong end as long as the switch is off.
Meanwhile, if your genset is TN-S and your house is TN-S and the changeover is how I'm doing it rather than the right way (Later...much later) then you'll be needing one of these too...
(and don't get too friendly with the genset chassis!)
We've had three days of power cuts and another coming on Monday.
Lead-Fi has been a trooper. Turns out it's AC coupling despite it's AJ 1300VA not officially having a charger...I've seen it charge up to 35A. The Sunny boy pushing 1700W will make it trip overtemp and then anti-island but handier with a little management than reconfiguring the solar array from 330Voc to 120Voc
Li-Fi made a guest appearance to bolster Lead-Fis charger and the next day charged off my hover van.
...and WuPoG sh1t the bed
I had it trying to synchronise with lead-fi as it says it can in the manual. 6A from the incomer and 10a from itself.
If you connect external power while the load exceeds 6A it will do this.
If you drop the load at any point it will sit there letting a 1300VA push 8A and just throttle it's charger.
Lead-fi tripped overcurrent, WuPoG bricked it's charger.
It's not coming back. I'm writing off ApprenticeVolt once and for all.
I spent €200 on an interface to edit the charger settings..it's just a teal RS232 to TTL
I spent €200 on a B-Type RCD because it's high frequency
I spent €600 on control gear because the charger is too slow & the alarm contacts and voltage protections don't work in any practical application.
Hrmmm I think I have a synopsis....
ApprenticeVolt recommends 35mm
2 cable for a 50A appliance and 6mm
2 earth which ought to light up nicely under a DC fault fused at 80A.
No sense terminals.
Charger derates above 57V
Inverter is 10A not 2500VA (2300VA at 230V)
Tail current setpoint does not work.
Charger is single-stage constant voltage.
Marketing says it's silent compared to low frequency. I measured 55dB last night of dubstep electronic noise and SanAce fans.
PE is relay switched
Load and SOC indicators are inaccurate.
Potential free relay is tied to the inverter shutdown threshold. You cannot start a genset with them until after the inverter sits down.
Over-voltage protection turns off the inverter but not the charger.
Monitoring voltage and current are inaccurate.
Voltage sense ±5%
Not galvanically isolated.
No surge capability.
2.5mm
2 throughput cabling rated at 50A
80% efficient.
Charger death with 50kWh on the Odo
€8 of lecky.
She's going into the pile of shame and I'm replacing it with a Studer XTM
This is the second time I killed it. The first I blew the H-bridge with about 4 hours on her.
Flimsey, lightweight shyte the hardware is 75% marketing.
Apple of power electronics.