Greetings,
Haven't had a chance to contribute much in recent times, but I've enjoyed following many of the stories posted. Our wind project has gotten delayed due to other priorities some of which are self-evident in the photo below (that & raisin' young'ns).

A couple years ago I bought a small Marathon water heater through a silent auction where I work. I finally got around to changing the port bushings and completing the wiring for use as an "opportunity load", as described more in the link below:
http://www.outbackpower.com/forum/viewtopic.php?f=29&t=2865&st=0&sk=t&sd=a&sid=d
cd929c9eb4286ca7289c42405b0267b&start=25

It is a slightly different approach to dump load charging for wind. The main difference is it really is looking at leveraging more PV potential. The controller connects the opportunity load to the battery bank and sustains it when it can by increasing array current, but the charge controller is still operating as the main charge regulation for the bank.

The basic concept is to send surplus power, once the batteries are satisfied, to a diversion load via a quasi-PWM signal. In this case the signal is 12VDC supplied by the Outback (MX60). The elements are 48VDC, interlocked and controlled via solid state relays. I'd been experimenting with it with a timer, and some manual intervention for a spell. We definitely record much higher kWh production with the diversion load. It's connected like this.


The two SS relays share one large heat sink. The left one controls the upper element; the right one is the lower.

The green indicator light on the side of the controller is an LED that I added to the "aux diversion" output of the MX60. When it is on, we're diverting energy to the water heater assuming the thermostat(s) is calling for heat. The relays also have LEDs, but they're out of site in the basement. In an effort to compensate for the tanks modest size, we're heating the tank to ~170F, and then supplying preheated water via a mixing valve to our instantaneous dhw heater (which modulates to meet the outlet setting).

Last night our water tank was ~160 degF. I've left the mixing valve at the factory setting, which is fairly low (~106F I think). So after our normal activities last night (dishes, clean up ,etc.), and two showers this AM, the in-coming water was still 90F. I've tweaked up the element temperature settings a bit more today, and anxiously looking to see how things go this week.
On a day like today (clear, sunny, and no one's home), it should allow us to squirrel away the equivalent of another 6-8 kWh, or roughly 25,000 Btus.

What I've also noticed is that there are conditions where the solar output is less than the diversion load, but the wind - we're still operating our trusty Scencenbaugh - is contributing enough to pulse the relay(s), so indirectly we're getting a bit more usable power from that as well.
Kind regards,
~kitestrings