If these are the big round cells, I've seen them on 48v (24 cell) CO systems and in 360v - 480v (180-240 cell) UPS aplications. One set I have been doing maintenance on was installed in 1979 and still had very good internal impedance and SG although the post to plate connections were beginning to deteriorate.
Some of these have ATT labels others have Tyco and Lucent. All have a model number KS-20472 and are rated at 1600+ AHr @ 8hr iirc. The older ones (List 1) had problems with the post to plate connections but they solved this with the later versions (list 2, 3, 4)
The Lucent owners manual mandates a float voltage of 2.17VPC but didn't specify an equalize value. The old ones ('79) have been kept around 65 - 68 deg for as long as I can remember. Some folks speculate these batteries could last 50+yrs due to the plate thickness and the stacked design of the plates that allows for expansion.
These would be my choice if money/space were not an issue as they are most definitely the best batteries I've seen in my 27yrs of UPS experience. Getting some for free would be like winning the lottery.
As with any flooded cell battery don't let them sit around uncharged for any extended period and check for sulfation (brown crystals) on the positive (black) plates. Sulfation can be reversed with equaliztion if it's not too severe.
Good find and good luck.
marv