OK, I spend the day testing and this is what I have found.
If I plug the slowpump in to any 110AC receptacle at the house, the electric motor spins fine, so I know teh pump is ok. But if I plug the same pump in to the plug at the pump house, it just hums. The difference is that the pump house is several thousand feet or so away from the inverter, and the 10/2 gauge wire down there that has been working for years and years I think can no longer keep up with the pumps needs. (we are off grid, not that it matters.)
I got some advice from a friend tonight and he suggested that since the pump is several years old that over time the pump is asking for more juice than the 1000 feet of 10/2 can provide.
He suggested I test this by.
Checking the voltage at the house, then testing the same voltage under the motor load.
Next do teh same thing down at teh pump house and see how the numbers compare. He is thinking that i will find that the pump under load at the pump house is requesting too much power and he has some charts to compare what is needed. I am thinking I might need a new pump to replace the old one.
I plan to do these tests in the morning, any other suggestions while I am at it?
I also posted a few questions / answers above, in case they help.
As always, thanks so much for your help.
- Shane