Wire loss calculation
« on: July 20, 2004, 09:47:45 AM »
hi all....


i've been trying to calculate the wire loss in a 3-phase wind generator...i expect 62 amps as maximum...the wires that i'll use are (each wire): 11 m of 2, 4mm wires joint together as to act as one wire..they have apprx. 1.5 ohms/1000m resistance, so for two wires joint together it will be 1.5/2 = 0.75 ohms/1000 m


i've seen Hugh's notes about line losses.....he explains how to calculate this loss and finally got to a formula:


loss (in watts) = (total amps)(total amps)(resistance in one wire)*2 (as i understood it)


so, concerning my machine:


resistance in one wire = (11/1000)*0.75 = 0.00825 ohms


so the loss = 62*62*0.00825*2 = 63.42 W


while somebody else ( i dont remember who ) said that we calculate the loss by:


loss (in W) = (2/3 * total amps)(2/3 * total amps)(resistance in one wire)


i  get : 41.3*41.3*0.00825 = 14 W loss!


so which way is right? or are they both wrong?!!! if so, how to calculate this loss


thx in advance

« Last Edit: July 20, 2004, 09:47:45 AM by (unknown) »

baggo

  • Jr. Member
  • **
  • Posts: 83
Re: Wire loss calculation
« Reply #1 on: July 20, 2004, 10:42:48 AM »
Hi edy252,


At a guess the first formula applies to DC current after the output is rectified.

The AC current in the alternator windings is not constant as the output is a sine wave.

Although I am no expert on AC theory I presume the average AC current in the windings is 2/3 of the peak current, hence the second formula.


John

« Last Edit: July 20, 2004, 10:42:48 AM by baggo »

Flux

  • Super Hero Member Plus
  • *******
  • Posts: 6275
Re: Wire loss calculation
« Reply #2 on: July 20, 2004, 11:06:59 AM »
Hugh is right

For normal rectifiers feeding a battery, current is carried in 2 wires, which swap round in sequence.  The loss is the same as DC but the heating is less as it is shared between 3 wires.

The rms AC current is 0.82 times the DC current.


Flux

« Last Edit: July 20, 2004, 11:06:59 AM by Flux »

wooferhound

  • SuperHero Member
  • ******
  • Posts: 2288
  • Country: us
  • Huntsville Alabama U.S.A.
    • Woofer Hound Sound & Lighting Rentals
Re: Wire loss calculation
« Reply #3 on: July 20, 2004, 01:33:53 PM »
« Last Edit: July 20, 2004, 01:33:53 PM by wooferhound »

edy252

  • Jr. Member
  • **
  • Posts: 54
Re: Wire loss calculation
« Reply #4 on: July 20, 2004, 11:40:28 PM »
hi...and thank you all for your replies.


what i didnt mention is that the rectifiers are 11 m AWAY from the genny, so the calculation of loss is for AC current going through these wires