AC DC conduit
« on: April 25, 2005, 06:41:16 PM »
Some advice needed, please.


What are the issues, if any, for running 240VAC single phase and 50VDC in the same 2" conduit?  They will be feeding waste loads for two different hydro systems.


--Douglas

« Last Edit: April 25, 2005, 06:41:16 PM by (unknown) »

Peppyy

  • Full Member
  • ***
  • Posts: 175
Re: AC DC conduit
« Reply #1 on: April 25, 2005, 01:23:52 PM »
I have heard that it is not a good idea due to the ac creating an inductive current into the dc wires. I am 99% sure the elecrtical code says it is a no no.


If it were me I would run them seperately.

« Last Edit: April 25, 2005, 01:23:52 PM by (unknown) »

Nando

  • Hero Member
  • *****
  • Posts: 1058
Re: AC DC conduit
« Reply #2 on: April 25, 2005, 01:24:24 PM »
Do not do it.


What is WASTE energy, ?? :-}


Regards


Nando

« Last Edit: April 25, 2005, 01:24:24 PM by (unknown) »

Victor

  • Jr. Member
  • **
  • Posts: 93
Re: AC DC conduit
« Reply #3 on: April 25, 2005, 01:53:13 PM »
Hi Douglas.


 In the U.S.A. this is allowed within the NEC ( national electrical code) provided that all wires have insulation rated to the highest voltage i.e. 300 volt insulation and that splices of the different systems are physically seperated via seperators within junction boxes or made in seperate junction boxes.


 There will be no problems with induced voltages etc.


Victor Creazzi

Aerofire Windpower

« Last Edit: April 25, 2005, 01:53:13 PM by (unknown) »

drdongle

  • Hero Member
  • *****
  • Posts: 552
Re: AC DC conduit
« Reply #4 on: April 25, 2005, 08:10:37 PM »
Dump load
« Last Edit: April 25, 2005, 08:10:37 PM by (unknown) »