While you can use a hall sensor - preferably in a clamp-on flux path - as a current sensor, there are other approaches.
For starters, why don't you use your cables as a shunt for a normal meter?
The cables have a cross section of 95mm sq.
Is that the copper cross-section, a measurement you took of the copper bundle, or a measurement of the wire and insulation?
What's the wire guage of the cables? (If 95 mm sq. is the actual copper cross-section it's somewhere between 000 and 0000, so I don't know what to make of your numbers.)
Here's some wire numbers:
gauge feet/ohm
0000 20402
000 16180
00 12831
0 10175
1 8069.5
2 6399.4
You can find more at this page for starters.
Assuming it's 000, you could open the insulation at two points 1.618 feet apart and solder on two small wires, and tape it up. That gets you a 1/10,000 ohm shunt (1 mv = 10A). Use a digital meter on a milivolt scale multiply milivolts by 10 to get amps. If the wire is long enough, do it 16.18 feet apart for a 1/1000 ohm shunt. Then milivolts -> amps directly.
Similarly for 00 you'd use 1.2831 or 12.831 feet, and so on.
Solder your instrumentation tap wires so the ends are running ACROSS the big wire rather than along it for best results. You can slide the wire back-and-forth to get the right position while the solder is being kept melted. (Don't sweat the resisitvity of the solder. It's high enough that the blob won't be a significant effect.)