I agree with Roy. The rating of these bridges is difficult at best.
The 35A is mean current with resistive or inductive load for operation in a single phase bridge and to get it you will need an almost infinite heat sink.
You may assume that building a 3 phase bridge and paralleling the halves of the single phase bridge you could double this current. In reality they will not share perfectly so that gives a derating. Additionally you have to transfer the heat to the heat sink and the package thermal resistance plays tricks that are not in your favour. Add to this the fact that the conduction time is very different for 3 phase rectified to a battery compared with single phase resistive loading you come off even worse.
The net result is that I think you are pushing your luck to get 35A dc from 3 of these bridges connected for 3 phase with wind operation even with a large heat sink.
24v 1kW is pushing your luck to the limit and if you get some big gusts that fool the furling you may go over the edge.
Also not all these things are created equal, you can push your luck with some manufacturers a lot more than others and if it was a product of Michael Mouse or some anonymous import it may never even manage 35A in its intended application.
Wise to play safe, probably cheaper than using more 35A units in parallel and a better solution.
Flux