48 cell panels any good for 24 volt system
« on: October 31, 2011, 07:08:53 PM »
Hi Guys,

I should know the awnser to this but am not to sure, working with grid tie systems all the time I tend not to worry about it due to MPPT.

I have some 48 cell panels at work with ~ 30Voc and ~24Vmp characteristics.

I want to use these on a 24 volt FLA system, will the panels in question work properly?


Many thanks

Jonathan


richhagen

  • Hero Member
  • *****
  • Posts: 1597
  • Country: us
Re: 48 cell panels any good for 24 volt system
« Reply #1 on: October 31, 2011, 10:51:45 PM »
Typically you would use what is basically the industry standard of 72 cells in series for charging a 24V lead acid battery bank, although I have seen old systems with as little as 60.  The reason for the overage is to have enough voltage to float or equalize the batteries in hotter weather when the voltage per cell decreases.  Your 24V flooded batteries should need about 29 or so volts into them to get fully charged in a reasonable amount of time, at which voltage, even in cold weather, the panels you describe will see much lowered amps.  Two in series with an adequate controller will work, but unless you have an mppt controller it is kind of a waste to have the extra cells above 72 in series as they will contribute essentially nothing to the performance. 