There are a lot of people out there that completely
freak out whenever you mention sla and equalizing in the same sentence... or storing a battery on concrete... or recharging alkaline batteries... etc.
The problem with equalization stems mostly from their definition of equalizing and what maybe should be referred to as conditioning instead.
Damon, I have a similar problem. One of the powered pallet jacks at work has 4 sealed golf cart batteries (24v setup), but the built-in charger only takes it to 25.3v
I checked today after a full day charging and each battery was 6.3 +/- very little. They all seem to have the same charge, but are not fully charged.
That lift never seems properly charged. It's only a year old. The battery gauge drops like a stone as soon as you use it. The cover comes off easy. Could I hook up a 12v car charger and equalize two at a time? What final voltage should it be 2 x 6v? I can trickle charge, I have a charger with a 2 amp setting.
dinx71, the bottom line ... find the specs on the batteries although it sounds like the charger is more at fault than the batteries.
If those batteries have been under charged for a year they may have permanently lost capacity.
There's more than one manufacturer of sealed batteries out there that recommend equalizing their batteries...
Concord (Lifeline VRLA): 8 hours @ 15.5v
Dynasty: 24 hours @ 14.4v
etc.
... find the specs.