Permission to take PV System to 5.16kWp
« on: January 21, 2010, 12:35:07 PM »
Hi,


I'd like to expand our grid-tie PV system once again to take up the remaining space on our small roof.


This would get us to over 5kWp of PV driving over 4.4kWp of inverters, though as the panels are on east- and west- facing roof surfaces it's virtually impossible for everything to be maxed out at once.


However, this expansion takes us over the 'G83' UK threshold where the local Distribution Network Operator (DNO) cannot refuse an installation, which stands at 16A per phase, 230V/240V.


So we've asked them nicely (well, the installer who's put in my first and second rounds did) and the DNO has given us the OK today.


Next up I have to convince my other half, the council because of covenants in our deeds rather than planning permission (though we might be getting big enough to have to consider that), my electricity supplier, and consider the complications of the new Feed-in-Tariffs coming in and the effect on a system spanning old and new schemes.  Indeed the new one might have to be considered entirely separate for simplicity.


However, at over 4kWp inverter output on a sunny day and (eventually) an 'instant' (air-to-water) heat-pump with a decent CoP, I reckon that we could match our current natural-gas hot water delivery (~24kW in, maybe 18kW out) directly from our panels with no grid draw and no carbon footprint!  Of course, at the other end of the year in winter, we might draw as much as 9kW from the grid to match our combi, but that's still OK.


So I'm very strongly leaning to finishing off with PV rather than doing any solar thermal, and also a bunch of 'Kingspan K-18' dry-lining.  My aim remains zero-carbon for primary energy.


Rgds


Damon


PS. I may also try to sneak a bit extra PV onto the roof for my off-grid system.  That may be tricky for various reasons though...

« Last Edit: January 21, 2010, 12:35:07 PM by (unknown) »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

zap

  • Hero Member
  • *****
  • Posts: 1107
  • There's an app for that
Re: Permission to take PV System to 5.16kWp
« Reply #1 on: January 21, 2010, 12:57:02 PM »
DamonHD Electric Generating Ltd.???


If/when you sell the house are you going to list it as a residence or as a "Power generating business with attached living quarters"?


Once you max out the space, what next? Nuclear?  DamonHD Industrial/Residential Flux Capacitors Ltd.?


I don't think we've seen any pictures lately?

« Last Edit: January 21, 2010, 12:57:02 PM by zap »

DamonHD

  • Super Hero Member Plus
  • *******
  • Posts: 4130
  • Country: gb
    • Earth Notes
Re: Permission to take PV System to 5.16kWp
« Reply #2 on: January 21, 2010, 02:18:53 PM »
Here's a pic of the front (2/3rds of the current grid-tie, about 2.6kWp):


http://gallery.hd.org/_c/mechanoids/_more2010/_more01/solar-panels-and-light-snow-and-sunshine-and-b
lue-sky-in-January-in-Kingston-London-England-2-DHD.jpg.html


A light dusting of global-warming flakes can be seen, beating back the photons...


I do hope that if/when we move that the PV system (and the house generally being zero-carbon and hopefully 'A' rated for energy efficiency) will add substantially to the house value, though who can tell these days where the (housing) market is going?


Rgds


Damon

« Last Edit: January 21, 2010, 02:18:53 PM by DamonHD »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

fabricator

  • SuperHero Member
  • ******
  • Posts: 3394
  • Country: us
  • My smoke got out again
Re: Permission to take PV System to 5.16kWp
« Reply #3 on: January 21, 2010, 03:07:31 PM »
WOW! That is a lot of hoops to jump through.
« Last Edit: January 21, 2010, 03:07:31 PM by fabricator »
I aint skeerd of nuthin.......Holy Crap! What was that!!!!!
11 Miles east of Lake Michigan, Ottawa County, Robinson township, (home of the defacto residential wind ban) Michigan, USA.

DamonHD

  • Super Hero Member Plus
  • *******
  • Posts: 4130
  • Country: gb
    • Earth Notes
Re: Permission to take PV System to 5.16kWp
« Reply #4 on: January 21, 2010, 11:18:40 PM »
Well, it isn't so bad.  And actually the local council has been quite helpful and keen; just got to see if this is a bridge too far for them or not...


Rgds


Damon

« Last Edit: January 21, 2010, 11:18:40 PM by DamonHD »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

Bruce S

  • Global Moderator
  • Super Hero Member Plus
  • *****
  • Posts: 5422
  • Country: us
  • USA
Re: Permission to take PV System to 5.16kWp
« Reply #5 on: January 22, 2010, 08:54:39 AM »
Damon;

I'm with ZAP on this one :).

Let me know before you start trading public shares, I'll dig out my shiny pennies and jump on that bandwagon <LOL>.


Pretty imperssive, how's the Chairman of the Board taking all this?


Cheers;

Bruce S


 

« Last Edit: January 22, 2010, 08:54:39 AM by Bruce S »
A kind word often goes unsaid BUT never goes unheard

DamonHD

  • Super Hero Member Plus
  • *******
  • Posts: 4130
  • Country: gb
    • Earth Notes
Re: Permission to take PV System to 5.16kWp
« Reply #6 on: January 22, 2010, 10:36:01 AM »
I am the sole director; much easier that way!


Rgds


Damon

« Last Edit: January 22, 2010, 10:36:01 AM by DamonHD »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

TomW

  • Super Hero Member Plus
  • *******
  • Posts: 5130
  • Country: us
Re: Permission to take PV System to 5.16kWp
« Reply #7 on: January 22, 2010, 11:18:00 AM »
HD;


So who is a the "soul" director?


Can't help it, I have this thing for play on words.


Tom

« Last Edit: January 22, 2010, 11:18:00 AM by TomW »

ghurd

  • Super Hero Member Plus
  • *******
  • Posts: 8059
Re: Permission to take PV System to 5.16kWp
« Reply #8 on: January 22, 2010, 11:29:59 AM »
Does "Mrs. Sole Director" know you said that???


« Last Edit: January 22, 2010, 11:29:59 AM by ghurd »
www.ghurd.info<<<-----Information on my Controller

DamonHD

  • Super Hero Member Plus
  • *******
  • Posts: 4130
  • Country: gb
    • Earth Notes
Re: Permission to take PV System to 5.16kWp
« Reply #9 on: January 22, 2010, 11:43:48 AM »
And the Company Secretary...


Rgds


Damon

« Last Edit: January 22, 2010, 11:43:48 AM by DamonHD »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

DamonHD

  • Super Hero Member Plus
  • *******
  • Posts: 4130
  • Country: gb
    • Earth Notes
Re: Permission to take PV System to 5.16kWp
« Reply #10 on: January 22, 2010, 11:45:07 AM »
You insensitive cad!  I'm in banking: I don't do "soul"!


Rgds


Damon

« Last Edit: January 22, 2010, 11:45:07 AM by DamonHD »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

veewee77

  • Full Member
  • ***
  • Posts: 244
Re: Permission to take PV System to 5.16kWp
« Reply #11 on: January 27, 2010, 08:00:53 AM »
I looked at the pics. Seems you are also growing biofuel on that roof! Look at all that grass!


:-)


DougS

« Last Edit: January 27, 2010, 08:00:53 AM by veewee77 »

DamonHD

  • Super Hero Member Plus
  • *******
  • Posts: 4130
  • Country: gb
    • Earth Notes
Re: Permission to take PV System to 5.16kWp
« Reply #12 on: January 27, 2010, 09:58:47 AM »
Sssssshhh!  Don't tell everyone!


Rgds


Damon

« Last Edit: January 27, 2010, 09:58:47 AM by DamonHD »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

Bruce S

  • Global Moderator
  • Super Hero Member Plus
  • *****
  • Posts: 5422
  • Country: us
  • USA
Re: Permission to take PV System to 5.16kWp
« Reply #13 on: January 29, 2010, 06:58:49 AM »
Are those dual Methane extraction vents I see? on the lower left?

B-)
« Last Edit: January 29, 2010, 06:58:49 AM by Bruce S »
A kind word often goes unsaid BUT never goes unheard

DamonHD

  • Super Hero Member Plus
  • *******
  • Posts: 4130
  • Country: gb
    • Earth Notes
Re: Permission to take PV System to 5.16kWp
« Reply #14 on: January 29, 2010, 09:52:09 AM »
Shhhhhhh, you're giving away all my secrets.


And yesterday I did sign up for Ecotricity's new "Green Gas" tariff, so maybe before long those 'flare vents' can be blocked off and redirected back into the gas mains.  "That's cooking on gas!" as the expression goes.  B^>


Rgds


Damon

« Last Edit: January 29, 2010, 09:52:09 AM by DamonHD »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

DamonHD

  • Super Hero Member Plus
  • *******
  • Posts: 4130
  • Country: gb
    • Earth Notes
Re: Permission to take PV System to 5.16kWp
« Reply #15 on: March 15, 2010, 03:10:41 AM »
New panels going up today...  (Removing existing panels on that roof, then redoing the frame to take all 12...  Scritchy noises above my head as I type...)  Local Building Control was getting a bit twitchy about the loading on the roof so we got a structural engineer in to verify that all was fine.


Not actually got a date to get the inverter and other A/C work done since hens have more teeth than suppliers have SMA inverters at the moment.  So just solar bling for a little while!


Rgds


Damon

« Last Edit: March 15, 2010, 03:10:41 AM by DamonHD »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

DamonHD

  • Super Hero Member Plus
  • *******
  • Posts: 4130
  • Country: gb
    • Earth Notes
Only the Paranoid Survive...
« Reply #16 on: March 15, 2010, 06:22:45 AM »
Good job I'm keeping a fairly close eye on this project.


On Friday when the scaffolding was going up I made a call to the subcontracted scaffolder (since I couldn't be at home) to make sure that everything was OK, and it was ... except for the fact that the scaffold was going up at the wrong house...  So they had to take it down again and put it up at my house this time.  %-P


Then, just checking with the PV install crew that they were putting up the agreed extra mounting rail for possible expansion of my off-grid system I got the "what extra rail?" response...  They are doing it at this very moment with good grace, it has to be said.  I may have rather delayed their lunch and robbed them of all their spares...


Anyhow, I have the whole of the existing PV system up and running again, hitting about 2kW now, but it'll be possibly a few weeks before my new SMA inverter is in and ready.  Guess who's gonna be the squeaky wheel until then?  B^>