Hi
I have three 113 Ah batteries on my system. I have noticed the capacity was dropping off for a while, I tried hitting them with the charger, the only problem I have is, the only chargers I have are multi stage charger conditioners which are OK on good batteries but start cutting back if the voltage gets to 14.5V.
So I started reading on desulphators and bought one. It arrived this morning and within half an hour it was connected across the battery and a charger was connected.
The little light came on and it whined, which I am led to believe means it was working. After a few hours my curiosity got the better of me. I realised it was no good looking on a meter to see what's happening, so out came the scope.
Battery 113 Ah VRLA
Meter Blue Point MT596A
Scope Tektronix 465 (100MHz)
Charger Protech 4 (Marine 4 stage charger conditioner)
At the time of the test the battery voltage was 14.53 the charger was on the float mode having been on for some 6 hours.
I connected the scope and set it up, it took a while to find the pulse rate but they were then clearly visible, A nice asymmetrical sine wave, the positive half cycle was +9V above base the negative part was -2.1 the first cycle had a duration of just under two divisions on the scope with the timebase running at .05uS per division with plenty of ringing.
All I can do now is be patient for three or four weeks then test the capacity again if it is OK do the same to the other two batteries. I wonder what success others on here have had with these things?
Brian