Why is this fuse blowing?
« on: April 01, 2020, 10:01:48 PM »
I have a bergey 10 KW unit here in Wyoming. I generate about 8,000 kWh per year and it has operated over 15 yrs with little maintenance.  There is a 35 amp fuse at disconnect at base of tower then about 600 ft buried run and a 50 amp fuse on same conductor at entry to inverter. I just blew the 50 amp fuse which is the second time in two years. I guess my question is why the 35 amp fuse is not blowing first. The 35 amp fuse has never blown.

Going to get a backup fuse (busman Fwh-50) butt maybe I should get a 60 amp....?

Andy

XeonPony

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 899
  • Country: ca
  • Sanity is over rated!
Re: Why is this fuse blowing?
« Reply #1 on: April 01, 2020, 10:48:15 PM »
No if it is blowing there is a reason for it. So some reason over 50 amps are getting pushed through that fuse to some where.

Do you have a camp on amp meter ?

Start tracing current flows. See if there was a defective batch of fuses, ambient temps, and such.
Ignorance is not bliss, You may not know there is a semie behind you but you'll still be a hood ornimant!

Nothing fails like prayer, Two hands clasped in work will achieve more in a minute then a billion will in a melenia in prayer. In other words go out and do some real good by helping!

SparWeb

  • Global Moderator
  • Super Hero Member Plus
  • *****
  • Posts: 5452
  • Country: ca
    • Wind Turbine Project Field Notes
Re: Why is this fuse blowing?
« Reply #2 on: April 02, 2020, 01:06:13 AM »
Wild a** guess #1:
Different fuses blow at different speeds. 
I can't really explain all the details but it is possible that a 50Amp fuse is so much faster than a different type of slow 35A fuse.
Wild a** guess #2:
There is enough capacitance in the buried 600ft run that when the inverter flips On, it accepts a momentary surge as the capacitor is discharged.
No one believes the theory except the one who developed it. Everyone believes the experiment except the one who ran it.
System spec: 135w BP multicrystalline panels, Xantrex C40, DIY 10ft (3m) diameter wind turbine, Tri-Star TS60, 800AH x 24V AGM Battery, Xantrex SW4024
www.sparweb.ca

adobejoe

  • Full Member
  • ***
  • Posts: 105
Re: Why is this fuse blowing?
« Reply #3 on: April 02, 2020, 09:37:29 AM »
Spar. I like your answer...capacitance in wire. The 35 amp is closer to the turbine so you would think that would go first.  I will keep a 60 amp spare. Thanks!,

DamonHD

  • Administrator
  • Super Hero Member Plus
  • *****
  • Posts: 4125
  • Country: gb
    • Earth Notes
Re: Why is this fuse blowing?
« Reply #4 on: April 02, 2020, 10:30:19 AM »
I find it difficult to believe that the energy stored in wire capacitance could even tickle a substantial physical fuse wire never mind get it hot enough to melt.

I'd be more inclined to believe a fast-blow vs slow-blow thing.

Or maybe there is some other curious intermittent wiring fault.

Rgds

Damon
« Last Edit: April 03, 2020, 03:21:47 AM by DamonHD »
Podcast: https://www.earth.org.uk/SECTION_podcast.html

@DamonHD@mastodon.social

SparWeb

  • Global Moderator
  • Super Hero Member Plus
  • *****
  • Posts: 5452
  • Country: ca
    • Wind Turbine Project Field Notes
Re: Why is this fuse blowing?
« Reply #5 on: April 02, 2020, 10:32:13 PM »
Try 0.3 uF per kilometer for dry wire.  The run is 600 feet so we have 2 conductors * (600*0.3048/1000*0.3) = 0.055 uF
That will store a micro Coulomb of charge.  It will discharge about 10 microAmps at 60 Hz. 

After a day to think about it, that's not it at all.

Can your wires handle the 60 Amps?
No one believes the theory except the one who developed it. Everyone believes the experiment except the one who ran it.
System spec: 135w BP multicrystalline panels, Xantrex C40, DIY 10ft (3m) diameter wind turbine, Tri-Star TS60, 800AH x 24V AGM Battery, Xantrex SW4024